We’ve just moved into a house that had a cable near the house terminated with a 3 pin plug and the other end came out in the garage 25 metres away. The idea was to throw an extension lead out of a window, plug it in and put a bucket over it to keep the rain off.
The cable was a good thick steel wired armoured one. But when it came out of the ground in the garage the cores were different colours. Somebody must have measured a bit short and made a join which is now somewhere underground. The cable they used to extend it is 110v. tool cable. Going straight in to a junction box with nice rubber insulated wires coming out. And when I did a Megger test (which should show a infinite resistance), let’s just say the readings were very finite 8) In other words, just plugging it in would act like under soil heating.
1st job was to rip it all out and start again with 6mm SWA, an MCB coming off the unprotected side of the CU in the house and a proper RCD protected CU in the garage.
Why unprotected? So if I get a short in the garage it doesn’t kick off the power in the house.