[Closed] Urgent boiler advice

11 Posts
5 Users
0 Reactions
48 Views
Posts: 49
Free Member
Topic starter
 

Had the boiler serviced last week and has been running fine. Just gone to bed and the system is making funny noises - checked the boiler and sounds like there is air in the system. But the boiler keeps running a cycle of firing up, running until it sounds like the air hits the boiler then shuts down. Then repeats.

I've turned the boiler off - does anyone know if this is OK without turning the gas off? The manual says when I shut it down to turn the gas off too but I don't know if this is for longer periods. I'll get the plumber round in the morning to look at it.

B


 
Posted : 22/11/2009 10:44 pm
 Bear
Posts: 2318
Free Member
 

Thata fine, just isolate electricaly and it will be fine.


 
Posted : 22/11/2009 10:45 pm
Posts: 49
Free Member
Topic starter
 

You mean unplug it?


 
Posted : 22/11/2009 10:47 pm
Posts: 0
Full Member
 

just unplug it, pilot wont light, gas valve will close


 
Posted : 22/11/2009 10:49 pm
 Bear
Posts: 2318
Free Member
 

If that is what will isolate it then yes. It will not be able to fire up with no electrical supply to it. (assuming it is a modern wall mounted boiler!)


 
Posted : 22/11/2009 10:50 pm
Posts: 49
Free Member
Topic starter
 

Yeah - modern wall mounted boiler. A ferroli.

Bit worrying since its in the kids bedroom 😕

Right gonna unplug it and go to bed.

Cheers


 
Posted : 22/11/2009 10:51 pm
 Bear
Posts: 2318
Free Member
 

that will be ok, get it checked out properly in morning, good luck, although sounds like nothing too serious (keeps fingers crossed for you!)

bad luck for having a ferroli tohugh!


 
Posted : 22/11/2009 10:54 pm
Posts: 49
Free Member
Topic starter
 

Are ferroli that bad??? Came with the house 🙁

Just got up and bleed all the radiators - one nearest the boiler let out air for about 60 seconds. Just turned boiler back on and gonna monitor it.


 
Posted : 23/11/2009 7:20 am
Posts: 4
Free Member
 

Topped pressure back up?


 
Posted : 23/11/2009 8:36 am
 jedi
Posts: 10238
Full Member
 

i was just going to recommend paulosoxo and he turned up 🙂


 
Posted : 23/11/2009 8:38 am
Posts: 49
Free Member
Topic starter
 

Yep, pressure was way down once the rad was bled so topped it back up to where it was before.

I think the problem was last night I realised one of the rads downstairs was off and had been for a long while - turned it on and thats when it started making the funny sounds.


 
Posted : 23/11/2009 10:37 am
Posts: 4
Free Member
 

Cheers Jedi! 🙂


 
Posted : 23/11/2009 11:47 pm