Usual “tool” for the job is a multi function tester. You should be checking the continuity of the CPC (earth). This can be done either as an end to end test with a long lead, or what is known as an R1R2 test where live and earth are linked and continuity checked. Figures should be recorded for the electrical installation certificate which is required for new circuits.
Also you should do an insulation resistance check. This is done L-E L-N N-E and confirms that the insulation in good condition. You should see 1M Ohm minimum but usually it’s >100M Ohms when testing good cable.
These tests are normally done after plastering but it’s not a bad practice to do so beforehand if time (and cost) permits.
Equally importantly a visual check should be made to confirm cables are in the correct zones etc. and a sanity check of the functionality to make sure you’ve actually run the cables required.
Light switches should ideally be no greater than 1200mm from floor level to meet building regs. If you’re thinking of fitting anything other than pendants it can be easier to wire “power to switch” rather than “loop in” to the ceiling as the connections are made in the switch box and fixing of light fittings is just 1 cable.
Also, I’d recommend 35mm back boxes (if you’re not using plasterboard boxes) as they will give more depth to work with, particularly if you choose to use anything other than dumb light switches. Leave the boxes about 2mm proud to allow the plasterer to skim to their edge.
Hope this helps.
Rich.
PS As mentioned above – no junction boxes which can’t be accessed for maintenance and inspection. All inaccessible joints should be permanent (ie crimped). Preferably no joints except at switches or in light fittings.