    Full Member

    Just preparing to board the ceiling in living room and noticed a random earth wire that appears to run out to the gas mains, dangling loose.

    This combination spells immediate death in my eyes; can I rectify this, or get a sparky in (previous one was pretty unreliable)

    Ta..

    matt_outandabout
    Full Member

    Run. Away.
    😀

    senorj
    Full Member

    It looks like the “tail” (the bit of tin with screws in) has fallen off the Copper pipe. Re connect it.
    edit – I would reconnect it somewhere it can be seen/inspected.
    Boiler inlet ? bath taps?

    nickjb
    Free Member

    Your water and gas pipes should be bonded to the earth on your meter. Previously pretty much all metal pipes were bonded but these days it’s just those 2. That connection may or may not be needed but it’s pretty essential that the cable from the gas pipe connects to earth on the meter

    bearnecessities
    Full Member

    Traced earth from fuse box and ended up here; masses of earth wire that goes nowhere and another earth that appears to go somewhere.

    One thing after a ******* another in this ******* house!

    I’ll try to get a new sparky; cheers.

    senorj
    Full Member

    Bummer . Looks like your spark “forgot” to do your earth bonding. Or left old stuff up there..(doesn’t look old though)
    Follow Nick’s drawing and you’ll be right.