So, here goes.

As part of the current house renovation project were putting power into the garage. The other day we wired up some LED lights in there and ran them from an extension lead from the house. Then we've installed 3 double sockets and a fused spur for an outside light. All connected to a brand new consumer unit with 6a breaker for the lights. A 16a for the sockets and spur and a 40a RCD.

Today we ran an armoured cable back to the house and have connected it to a spare 40a breaker in the house consumer unit.

All good so far. But put any load on the garage, ie. Switch on lights or try to use a socket and the 63a RCD in the house trips immediately.

We've gone back through all cabling. Tried a new 40a breaker in the house. New RCD in the house and also new RCD in the garage consumer unit.

Nothing seems to work. The brother in law is a qualified spark who's been here all afternoon installing this with me and even he's stumped, although he's more used to industrial 450v stuff, he can't believe he can't suss it out.

Anyway, we've given up for the night as we're cold and fed up and he's gone for a think. But in the meantime I thought I'd run it by the STW hive mind to see what comes out.

Cheers


 
Posted : 18/12/2019 4:14 pm
Posts: 0
Free Member
 

Sounds like everything worked fine till the armoured was installed?

If so then could be that there is an issue with the termination of the armoured cable, the wiring arrangement in the garage or that the earthing is picking something up from that end. Id start investigating there. Not sure whats around your garage, if its close to another installation

Could be worth installing a single way consumer unit that is fed before the main RCD in the house and install an RCD at the garage


 
Posted : 18/12/2019 4:19 pm
Posts: 0
Free Member
Topic starter
 

We've checked that the Armoured is terminated properly at both ends. Even belled through the cable to check for short circuit or anything. Wouldn't expect us to be able to switch on the breaker in the house if there was a short anyway. But we checked all the same.

Until we try and switch anything on it sits there showing 240v out onto the circuits, but turn the lights on or plug something in and off goes the RCD in the house.


 
Posted : 18/12/2019 4:26 pm
Posts: 5750
Full Member
 

Check you haven't wired the neutrals in the new/old consumer correctly. I remember having the same issue years ago and it was due to one wire being wired into the neutral bus bar on the wrong side of the RCD. Can't remember off the top of my head exactly which one but it was obvious when I cast a critical eye over it. I only discovered the solution by phoning a mate who was a sparky and he instantly knew the answer as it seems to be a rite of passage, ie. everyone does it wrong at least once.


 
Posted : 18/12/2019 4:27 pm
Posts: 0
Free Member
Topic starter
 

Just reading that is it because we have two RCD in the equation?

Maybe we should take our feed from the other side of the RCD in the house as the garage has its own RCD anyway?


 
Posted : 18/12/2019 4:29 pm
Posts: 0
Free Member
 

What happens if the main switch in the garage and the MCB's in the garage are on on but nothing plugged into the sockets and no lights are switched on?


 
Posted : 18/12/2019 4:31 pm
Posts: 0
Free Member
 

The two RCD's shouldnt cause the other one to trip. Its not ideal to have two RCD's in series unless one has a time delay on it, otherwise an issue in the garage will trip the house. Inconvenient and potentially expensive, freezer, central heating not able to work


 
Posted : 18/12/2019 4:33 pm
Posts: 0
Free Member
Topic starter
 

@turin breakers and RCD in the garage turned on but nothing plugged in and lights not on and it sits there quite happily. We have tested and there is 240v output from the breakers.

@welshfarmer don't think it's possible on this consumer unit. Live and neg feed into top of RCD. Preinstalled cable from N output of RCD to N buzzbar. Copper bar from L side of RCD to input for breakers.

Just been and checked that no neutrals have strayed into the adjacent earth bar.


 
Posted : 18/12/2019 4:37 pm
Posts: 2642
Free Member
 

Check you haven’t wired the neutrals in the new/old consumer correctly.

+1

Sounds like you've got a split load CU in the house and you've taken the line (live) from the RCD protected side of the house CU and returned the neutral to the non-RCD side of the house CU - every time you draw a load the house RCD senses an imbalance and trips off.

Best to take both line (live) and neutral from the non-RCD part of the CU. Otherwise make sure that the neutral from the shed is also returned to the RCD protected neutral busbar.

Edit to add (as I've just seen your last reply) it could be a neutral-earth fault in the shed wirin, but your qualified sparky should have tested for that before connecting it all up.


 
Posted : 18/12/2019 4:42 pm
Posts: 0
Free Member
 

Its hard to tell remotely but things that spring to mind

COULD be a faulty RCD at the garage - only causes an issue under load, but if it trips immediately this is unlikely. Can the RCD at the garage be swapped for a main switch? If that fixes it and you want RCD protection then you could install RCBO's in the garage

If it was my house id have the supply to the garage fed from a point before the house RCD.

Has the BIL tested the installation? not meaning to sound liek a dick but often people wire and switch on and dont do any testing before or after installation.

Edit - what Tillydog says could be spot on, if you have dual RCD's in the house?

EDIT 2 - in turn completely disconnect the 3 wires from each mcb at the garage and try to energise, that should help focus where the issue is


 
Posted : 18/12/2019 4:44 pm
Posts: 3816
Full Member
 

Have you checked all the wiring to the sockets?
Are they wired on a ring or radial? If on a ring you could try dropping each socket off the ring in turn and seeing if that's causing an issue.


 
Posted : 18/12/2019 4:54 pm
Posts: 0
Free Member
Topic starter
 

@dirkpitt74. The sockets are on a radial. Just one single and a pair of doubles.

He's checked / tested the socket and lighting cabling and we also know the lighting worked when the cable from the switch had a plug on the end connected to an extension lead.

Have sent the BIL some of these replies to see if he has any lightbulb moments.

For me now I'm off to freeze my dangly bits off for a couple of hours on the bike.


 
Posted : 18/12/2019 5:04 pm
Posts: 0
Full Member
 

My garage is fed from the house before the house CU. If a fault in the garage it doesn't affect the house.

Starting with that would also isolate or eradicate your problem.

My practical but non sparky brain would disconnect at the house end, then put a temporary extension lead to the garage CU fed from a house socket. If it fails on load then that points to a fault in the garage. If not then it's the garage feed.

Just shows how even a pro sparky dealing with something outside of their normal remit can miss something.


 
Posted : 18/12/2019 5:04 pm
Posts: 775
Free Member
 

Sparky here.

Easy to get tied in knots looking for these type of faults, actually its normally straightforward to sort providing you approach logically.

The difficult bit is gently approaching your BiL with the following advice*

1. Disconnect the supply
2. Grab a copy of Guidance Note 3 and follow the tests in the correct order, dead tests first

Sounds like a bit of an arsey answer, but there is a very good reason to do the above (and understand what your doing and why)


 
Posted : 18/12/2019 5:25 pm
Posts: 0
Free Member
 

if the rcd is not tripping on energization , but only when "under load" , £5 says the swa cable is connected to the wrong neutral bar in the house C.U. , or a similar wiring fault at the garage

we've all done it whilst tired or rushing near the end of  a tough day  🙂


 
Posted : 18/12/2019 7:40 pm
Posts: 4954
Free Member
 

Isolate each bit of the circuit in sequence. Rewire with a dummy circuit as you have the sea so you can easily move things around to test.

I am out of touch with latest reg but there was a requirement for discrimination between rcd's if in series. Easiest way was to have a 100ma supply and 30ma closer to the load.


 
Posted : 18/12/2019 8:01 pm
Posts: 0
Free Member
 

Qualified sparky here own a contracting firm that specialises in inspection and testing....what you’ve got is a neutral fault.

Couple things to try, turn new CU off and have sparky do a loop test on the armoured cable, this’ll prove the swa can take a load. Make sure loop tester is on RCD setting so it doesn’t trip the house. After you’ve proven this double checking no cores have been crossed and same colours been used at both ends you can then connect in one circuit at a time. Tbh had the new install been fully tested first this wouldn’t have happened but you can rewind and do that now 👍


 
Posted : 18/12/2019 9:47 pm
Posts: 1726
Free Member
 

You can randomly check possible/probable causes (I am betting neutral fault)

Or you could test/diagnose the fault.


 
Posted : 19/12/2019 12:05 am
Posts: 0
Free Member
Topic starter
 

@tillydog and @brownsauce win the prize (qudos)

Was just the neutral in the wrong non RCD bar in the CU.

Took 1 minute to check and correct. I'm blaming the fact that we'd frozen our bits off pulling the armoured through in sub zero conditions that our brains no longer worked.

Cheers! STW for the win yet again.


 
Posted : 20/12/2019 1:25 pm
Posts: 5750
Full Member
 

Ahem, I think I win the prize too! 🙂


 
Posted : 20/12/2019 10:58 pm
Posts: 0
Free Member
Topic starter
 

@welshfarmer haha, ok I'll give you that now I've been back and read the post again. 👍


 