[Closed] Central Heating Experts - why are my pipes banging?!

Posts: 17846
Full Member
Topic starter
 

No probs....

Yeah, I like back to basics...'easy' things to do:

- check boiler stat setting & measure output boiler temp.
- look for obvious faults with system; integrity of cylinder stat etc.
- check 'balance of system' and adjust if required.
- try 'purging air' from radiators as spooky b329 suggested, for the sake of being thorough.
- look for loose pipework.

I appreciate all the help. I will post an update once I have done some stuff. Probably won't be until after the weekend though.

I live near Peterborough (I must have sinned in another life! ๐Ÿ˜‰ )


 
Posted : 23/11/2011 1:35 pm
Posts: 0
Free Member
 

Yes, it sorted the noise...... Balance the system first as you need the water to flow evenly throughout the system.

Good luck!


 
Posted : 23/11/2011 2:03 pm
 Bear
Posts: 2351
Free Member
 

Stumpy

I have found to lag the pipes and wrap a clip over the top to be best, waste pipe clips fit pipe lagging well or fixing band.

And nothing wrong with Sentinel, good product (nothing wring with Fernox either but years ago one of their product affected the balls in Honeywell motorised valves)


 
Posted : 23/11/2011 8:19 pm
Posts: 18593
Free Member
 

What about the speed setting of your circulator pump. Pumps are usually two or three speed and position 2 will be all you need on the three-speed pump.

Spending the money on isulation rather than new radiators would have perhaps been more profitable.


 
Posted : 23/11/2011 8:59 pm
Posts: 0
Free Member
 

money on new panel rads is never wasted.. they use much less water and benifit from both radiated and convected heat plus you get the trv.. so for 150/200 fitted they are excellent value.. insulating pipes has value but they do provide heat where there are no rads..


 
Posted : 23/11/2011 9:11 pm
Posts: 18593
Free Member
 

I meant insulating the house so you don't need as much heat.


 
Posted : 23/11/2011 9:19 pm
Posts: 0
Free Member
 

Two things made my pipes bang; iffy motorised valve or a drained header tank. The ball valve on my header tank sticks in the summer due to no usage and limescale buildup so the tank drains and doesn't refill. A quick nip up to the loft each autumn to free it up cures the problem. Otherwise the system drags air in rather than water and that air gets trapped in the system and causes the pipes to bang as it is dragged round.


 
Posted : 23/11/2011 9:21 pm
Posts: 3404
Full Member
 

@stumpy01

If you are referring to spooky b329's post, he was referring singularly to TRVs not plurally, apart from one occasion. And if you are referring to the apostrophe he used for the plural of TRVs, it is grammatically acceptable to add an apostrophe to an acronym for the sake of clarity.

Dear oh dear. The plural of TRV [b]is[/b] TRVs, even in 2011. TRV's is a possessive: e.g. 'the top of the TRV'. Or worse, that crime of crimes, a grocers' apostrophe - used by grocers rather than an individual grocer. Not that I'll get much support from Stephen Fry on this subject these days if he's in one of his 'anything goes, the language is evolving' moments.

TRV is an abbreviation or 'initialism'. An acronym is an abbreviation that forms a name e.g. BOB - bag of bolts.


 
Posted : 23/11/2011 9:28 pm
Posts: 3404
Full Member
 

my pipes bang gently just near the wall of my bedroom every time the heating comes on. And all thanks to the excellent installer way back when who drilled a 15mm or 16mm hole through the joists to accommodate a 15mm copper pipe. I'm guessing that as the pipe expands slightly and tries to move a little through the joist it drags and then moves. 'bang, tap, tap, tap, tap, bang...'. It eventually settles down. Sometimes just before the heating goes off.


 
Posted : 23/11/2011 9:31 pm
Posts: 0
 

Apologies for not reading all the replies: I had a similar noise which was fixed by smoothing the notch where a pipe went through a joist, and padding it with a cloth.


 
Posted : 23/11/2011 10:51 pm
Posts: 17846
Full Member
Topic starter
 

Bear & slowoldgit thanks for the suggestions to seat the pipes.

Edukator, you are assuming I haven't added copious amounts of insulation to the loft AS WELL as replacing the rads. Which I have. I have also bought thick curtains to reduce heat loss through the windows. I also considered cavity wall insulation but have decided I need to look a bit more into it.

OH's dad recommended new rads after how ineffective the old ones were last winter. He used to install the ones that were fitted & reckoned that while they were good in their day, modern rads fitted with convectors are much more effective. As totalshell says above.

And I have tried all 3 pump speed settings. It makes no percievable difference.

Souldrummer - thanks. I have seen sticking ball valves mentioned elsewhere too (& motorized valves) so will be adding those to my list of things to check.

Prettygreenparrot - thank's for contributing too this thread. You're grammar lesson & interesting tail about a banging pipe has helped me know end.


 
Posted : 23/11/2011 11:34 pm
Posts: 1933
Full Member
 

new idea!
I've had problems with Honeywell TVRs; they are supposed to be bi-directional, but aren't. lift the floor boards near the offending rad and swap over the flow and return at a joint,or put the valve from vertical to horizontal (or vice versa).


 
Posted : 24/11/2011 12:00 am
Posts: 18593
Free Member
 

How about insulating under the floor and doing the walls on the inside? The only heating system in the room I'm in is from the TV, amp, computer and strip light; the radiator that was in the room is rusting in the shed.

How much is "copious"? You need 40cm in the roof for "passive house" standards.


 
Posted : 24/11/2011 8:17 am
Posts: 17846
Full Member
Topic starter
 

chickenman - Member
new idea!
I've had problems with Honeywell TVRs; they are supposed to be bi-directional, but aren't. lift the floor boards near the offending rad and swap over the flow and return at a joint,or put the valve from vertical to horizontal (or vice versa).

Oh! When you say 'they aren't' how does this problem manifest itself? If the TRV is fully open - i.e. rotated to number 6 on the knob, does it not just run as an open valve? Would this cause the problem? I thought the problem with running TRVs in the wrong direction is just when they are closing/opening??
I am not saying you are wrong, but I am just trying to understand how this would cause the problem. As mentioned somewhere above, we have run all radiators with TRVs fully open & also with the two radiators near to where the problem is, fully closed and the problem persisted in both cases.

Edukator - Member
How about insulating under the floor and doing the walls on the inside? The only heating system in the room I'm in is from the TV, amp, computer and strip light; the radiator that was in the room is rusting in the shed.

How much is "copious"? You need 40cm in the roof for "passive house" standards.

Edukator, ideally I would like to add more insulation. When we get round to decorating the rooms, we will consider insulation requirements in turn. But, I am not considering ripping up floors or insulating walls on the inside at the moment; particularly the walls if we end up getting cavity wall insulation.
As I said before, I have read pros and cons about cavity wall insulation and would like to find out more for our particular application before going ahead with it.

With regards to loft insulation, we have a shallow pitched roof and at the extremities of the pitch, I have filled the void completely (while still allowing an adequate ventilation gap). Further in, there is the depth of the joist insulated which was there already, plus an extra 250mm that I have added taking it up to about 320-350mm. There is an area of laid boards that we are using for storage. Originally this extended the full length of the roof, but I have substantially shortened this to only the length I envisage we will need for storage. This area has joist depth insulation and the area that I have decided we will no longer use for storage has had the insulation increased to ~320-350mm depth.
Even with all this insulation though, the pipes are still banging so it's largely academic!


 
Posted : 24/11/2011 10:41 am
Posts: 0
Free Member
 

Stumpy.
I like the cut of your Jib, make a list and check each item one by one. A methodical approach always pays-off in the end with things like this.

Insulation is always a good thing but in this instance totally academic. It wont stop the banging noise.

TRV's They can still shut even on maximum setting. To discount them remove the heads, then test.

Expansion of the pipes is the most likely cause by far (32 Yrs in the business).

Good luck, keep us posted.


 
Posted : 24/11/2011 12:52 pm
Posts: 0
Free Member
 

i would disagree with the expanding pipes theory, why did'nt it do it before? only the rads and some wiring have been changed. IMO its most probably air, thats what causes the clanging noise. i would check all the high points in the pipework for air release valves. usually hidden in a loft or above the boiler if the pipes rise from the top. there may be an air release valve on the flow going to the cylinder coil. there may be an automatic air release valve in the boiler itself which has been closed.

do the pipes from the rads go down through the floors, or do they drop from above?


 
Posted : 24/11/2011 8:55 pm
Posts: 17846
Full Member
Topic starter
 

supremebean - Member
i would disagree with the expanding pipes theory, why did'nt it do it before? only the rads and some wiring have been changed. IMO its most probably air, thats what causes the clanging noise. i would check all the high points in the pipework for air release valves. usually hidden in a loft or above the boiler if the pipes rise from the top. there may be an air release valve on the flow going to the cylinder coil. there may be an automatic air release valve in the boiler itself which has been closed.

do the pipes from the rads go down through the floors, or do they drop from above?

Sorry, I missed your post.
I am hoping it's air to be honest, but it does sound like the same pipes that are causing the noise (airlock, perhaps?).
I understand what you mean about it only being the rads & wiring changes, so why would the pipes start clanging when they weren't before. My thinking was that the old rads were imperial & the piping to them sized, as such. When we replaced them, we got the closest size radiators we could and my OH's dad had to do a bit of re-piping etc. to get the new ones to fit.
I wonder if in doing so he has disturbed a pipe that was perhaps not held very well and is now freed up.

I will check for an air release valve. There is not one obviously coming out of the boiler.

All of the rad pipes come up through the floor.

This weekend is going to be fun fun fun!!


 
Posted : 25/11/2011 4:23 pm
Posts: 0
 

You mentioned disturbing the pipe while changing something. I believe that's what happened to me, with a radiator replaced by a towel rail needing wider spaced pipes. It could have been that the fitter bent the pipe where it passed thru the notch. It was obvious where it had been rubbing, once I got the floorboard up.

With the older rads, maybe the flow was slower and the temp. rise and expansion in the pipes more gradual.


 
Posted : 25/11/2011 7:50 pm
Posts: 17846
Full Member
Topic starter
 

- check boiler stat setting & measure output boiler temp.
- check motorised valve
- check ball cock in roof tank
- look for obvious faults with system; integrity of cylinder stat etc.
- check 'balance of system' and adjust if required.
- try 'purging air' from radiators as spooky b329 suggested, for the sake of being thorough.
- look for loose pipework.

So then....

We turned the heating off on Friday night & just had the hot water left to come on in the morning. Completely silent on Saturday morning.

- Stupidly I forgot to get a thermocouple from work, so we didn't have any way to check the boiler outlet temp, but it didn't seem to be getting too hot & boiling.....
- Motorised valve seems to be working OK.
- Ball cock is working in tank, definitely.
- No 'obvious' faults, cylinder stat appears to be fitted well & securely. The water from the taps doesn't get stupidly hot, so presumably it is working OK. Also found what I think is bleed pipe coming from the cylinder (short vertical pipe tee'd off the cylinder with a knurled copper knob on top). No air came out of this.
- Didn't get round to checking system balance as I had no means to measure temperature.
- Tried Spooky B329's method of purging air. It seemed to reveal a couple of things. There was a gurgling, surging noise from a couple of radiators upstairs. But not the ones that we think are causing the problem. The boiler cut-out at one point, even though the thermostat set-point hadn't been achieved in the living room. I think this is due to the flow being restricted, so the system got too hot. The pump carried to run until the system had cooled a bit and then the boiler lit itself again. Upon opening the valves to the radiators that we thing are causing the problem, there was an almost immediate clonking noise, but there was little/no gurgling or other sound to indicate that air was being purged from the system. Indeed, upon letting the whole lot cool down & putting the rad valves back to normal, I re-bled all the rads and absolutely no air came out.

Next stop is to dig up the floor boards, which I am trying to put off! Gonna have to face it at some time.....


 
Posted : 28/11/2011 10:45 pm