  • OrmanCheep
    Free Member

    I have a little maths problem at work, which I am hoping one of you may be able to help with
    I have an equation…

    x = ((thi – tco) – (tho – tci)) / ln((thi – tco)/(tho – tci))

    where
    x = LMTD (log mean temperature difference in a heat exchanger).
    thi = temperature of hot fluid in
    tco = temp cold fluid out
    tho = temp hot fluid out
    tci = temp cold fluid in

    Now, I know LMTD, and thi, tho & tci

    I just need to rearrange the equation to use in excel so that I can calculate tco directly without having to resort to a goal seek.

    Thing is, I haven’t got a clue how to rearrange the equation.
    Any help greatly appreciated!

    gonefishin
    Free Member

    As tco appears twice in that formula, and once within a ln function, I’d use goal seek.

    Incidently you have allowed for the correction factor to allow for the fact that the exchanger won’t be true parrallel counter current flow?

    OrmanCheep
    Free Member

    Cheers gonefishin, but the goal seek is the bit I am trying to get rid of. I presume that because it is solvable, there must be some way of rearranging to calculate directly. Long time since my A-level maths though.

    Hadn’t considered a correction factor (yet) – cheers, I’ll look into it.

    Once designed and built, this condenser will be condensing single malt whisky, which gives me a vested interest in getting this right 🙂 !

    TiRed
    Full Member

    OK, here’s what I would do…

    Transform your variables so that z = x/(tho – tci) and y = (thi – tco)/(tho – tci)

    Then your equation is z = (y-1)/ln(y)

    which requires you to find the root of y – z ln(y) – 1 = 0

    Mathematica has an approximate solution for this root, which is

    y = -z W(-exp(-1/z)/z)

    where W is the Lambert W function. You could use the series expansion of W for this as follows;

    Let a = -exp(-1/z)/z

    then y = -z W(a)
    W(a) = a – a^2 + 3 (a^3)/2 – 8 (a^4)/3 + 125 (a^5)/24 +…

    you will then back transform y to get tco. Define a new column in XL for each transformed variable.

    Or use Goal seek 😉

    gonefishin
    Free Member

    I doubt you’ll be able to get it into a discrete solution, it’s not always possible and sometimes iteration is the only way to go. I think by rearranging it you will end up with something like

    tco + e^(tco + x) = Function

    which isn’t that much more helpful.

    Whenever I’ve come up against this issue with heat exchagers I use goal seek (or an interative solution if excel isn’t available). Well I did until I got access to exchanger sizing software at work.

    OrmanCheep
    Free Member

    OK, here’s what I would do…

    Transform your variables so that z = x/(tho – tci) and y = (thi – tco)/(tho – tci)

    Then your equation is z = (y-1)/ln(y)

    which requires you to find the root of y – z ln(y) – 1 = 0

    Mathematica has an approximate solution for this root, which is

    y = -z W(-exp(-1/z)/z)

    where W is the Lambert W function. You could use the series expansion of W for this as follows;

    Let a = -exp(-1/z)/z

    then y = -z W(a)
    W(a) = a – a^2 + 3 (a^3)/2 – 8 (a^4)/3 + 125 (a^5)/24 +…

    you will then back transform y to get tco. Define a new column in XL for each transformed variable.

    Or use Goal seek

    😯 Holy batshit 😯 . Goal Seek it is then.

    Cheers for the help chaps.
    First two drams will be yours. Should be ready in 2027.

    TiRed
    Full Member

    Post up your numbers for the four known values and I’ll knock up a quick worksheet to test the solution validity. I know nothing about heat exchangers, but I do know a little maths!

    OrmanCheep
    Free Member

    Thanks RedTi,

    LMTD is 14.6°C
    thi = 95°C (boiling whisky)
    tho = 85°C (condensed whisky)
    tci = 18°C (cooling water from the river)
    tco = unknown (hot cooling water)

    using goal seek, I get tco = 94.285°C

    Much appreciated.

    gonefishin
    Free Member

    Well that might work mathematically but your temperature approach is way too close to work in practice. A thi of 95 and and tco of 94 (realistically you won’t be able to measure anything more accurately than 1 C) will give you a major problem.

    Are you sure your LMTD is 14.6?

    OrmanCheep
    Free Member

    The LMTD is correct for the temperature values I have taken, based on an estimate of the U value and heat transfer area.
    The condensers are made in one size only, so the area will be fixed and non negotiable (I just don’t know what that area is yet).
    I will be calculating a more accurate U value later, but for now, I am just building up a spreadsheet, and want to get the mechanics right before tweaking the numbers so that they make sense.
    I used 3 decimal places, purely because that was the output from the goal seek – not because I want to achieve that level of accuracy!
    I am actually expecting tco to be around 75°C in reality.

    gonefishin
    Free Member

    Ah right. If the exchanger is oversized for its duty, which would appear to be the case here, then high cooling water outlet temps will always be the result. On the plus side it will likely foul up pretty quickly which will bring the cold outlet temperature down a bit. 😉

    OrmanCheep
    Free Member

    Ah, they do have fouling issues (especially with the water coming straight from the Spey).

    They run this way to deliberately produce hot water, so that they can use it to pre-heat the feeds to the Stills. It is not the most efficient method for them to be recovering heat, but it is their process, and getting them to consider new approaches is nigh on impossible. “It may change the character of the whisky” is the response to all process improvements I’ve recommended so far. Fair comment, but frustrating!

    Smudger666
    Full Member

    ormancheep

    thread hijack

    I’m working with some distilleries regarding integration of biomass steam boilers into their processes – is this anything your distillery has considered?

    email in profile

    /thread hijack

    OrmanCheep
    Free Member

    Hi Smudger,
    Yes, they are intending to use a remote steam supply from a stand-alone biomass boiler. Possibly one one of yours I imagine!

    Smudger666
    Full Member

    which distillery?

    OrmanCheep
    Free Member

    emailed you.

    Smudger666
    Full Member

    nothing received?

    jambalaya
    Free Member

    @Oman, just programme up @TiRed’s suggestion. Spreadhseets are good for doing this sort of thing even if it looks complicated posted here. For a “belt and braces” check you should do the calculation both with the formula and goal seek and check the results are close.

    TiRed
    Full Member

    Pretty accurate 😉 . I also have a plot of tco vs. X for all values of X (1-25)

    x 14.6 Log Mean temperature difference in heat exchanger
    thi 95 Temp hot fluid in
    tho 85 Temp hot fluid out
    tci 18 Temp cold fluid in

    z = 0.217910448, z = x/(tho – tci)
    a = -0.046636583, a = – exp(-1/z)/z
    W(a) = -0.048977467
    y = 0.010672702, y = (thi – tco)/(tho – tci)
    y(thi-tco) = 0.715071022
    tco = 94.284929, Closed form solution
    tco(goal) = 94.284927

    Need your email address for the solution, mine’s in my profile.

    TiRed
    Full Member

    General solution for your parameters:

    You’ll need an X of about 40 to get to a tco of 75 degrees (note the semi-log plot).

    OrmanCheep
    Free Member

    I like them apples 🙂

    I’ll email you now. Thanks very much.