hope somebody can help me with this, otherwise i'll be driven to asking on one of those electronics geeks forums...

i bought a digital 1ph 220V to 3ph 220V converter on ebay to run a dual voltage motor, ie one that can does 380v or 220v .
got it all hooked up in the end after a very chinglish instruction manual and the motor spins up to speed ok, or seems to, but is completely lacking power. attachign the drive belt to it causes it to stop almost completely.
voltage between phase reads about 80V, which is right yeh? a third of 220ish?
but output voltage on the digi thing says 36 volts or so.
max voltage is setable and is set right to 220.

there we go anyway. i can't fathom it. any help would be great.


 
Posted : 20/07/2015 5:56 pm
Posts: 1409
Free Member
 

Could be wrong, but line to line voltage (ie between phases) should be higher than line neutral? But probably depends what you're measuring it with.


 
Posted : 20/07/2015 6:13 pm
Posts: 0
Free Member
 

When im testing 415v 3phase, each leg to the winding is 220v to earth and between the windings is 415v, what have you got to earth from the motor terminal?


 
Posted : 20/07/2015 6:22 pm
Posts: 0
Free Member
Topic starter
 

ah ok, i'll check some things.
it's wired in delta so there's no neutral

so at 220v 3 ph what should it be between phase and earth christian? any idea?


 
Posted : 20/07/2015 7:37 pm
Posts: 0
Free Member
 

Line to line voltage is about 1.7 times the line to neutral voltage.

Its worth noting that a digital volt meter wont read correctly as the voltage waveform will not be sinusoidal. If you want to measure the true output voltage you'll need a oscilloscope I'm afraid.

Can you give me a link to the manual for the unit to have a look at?


 
Posted : 20/07/2015 7:44 pm
 igm
Posts: 11874
Full Member
 


When im testing 415v 3phase, each leg to the winding is 220v to earth and between the windings is 415v, what have you got to earth from the motor terminal?

415V 3ph = 240V ph-earth I hope
400V >> 230V and so on

square root of 3 being around 1.73 and all


 
Posted : 20/07/2015 7:47 pm
Posts: 0
Free Member
 

220v three phase should show 220v between phases, as 415 shows 415 between phases, to earth probably 120v. dont work on 220v three phase myself but principle is the same. seems like the output to the motor is low as the unit is telling you which is why it has no torque, surpised its turning at all if thats the case mate!


 
Posted : 20/07/2015 7:54 pm
Posts: 0
Free Member
 

Not quite, the 220v is line to neutral I.e. star connection so if you could measure the voltage across the outputs you should see 380v. But a mentioned above you can't do this without a scope (the output is a square wave, so a standard RMS algorithm like virtually all multimeters use doesnt work)

My initial guess is that the inverter is current limiting its output.


 
Posted : 20/07/2015 8:01 pm
Posts: 0
Free Member
Topic starter
 

ok great, thanks a lot everyone.
yes i figured it was low volts to motor giving low torque.
still haven't checked voltages cos i'm lurgied up but will do with an needle type meter if that works

dvatcmark, it's this one :
http://www.ebay.co.uk/itm/251389853828
quite q lot of info there within the listing.
i notice it says "single phase connected to any 2 phases" under [i]How to install this VFD[/i]
i've got live and neutral of supply just to one terminal each at R-S-T in diagram. should i try bridging 2 together from live? guess i should.


 
Posted : 20/07/2015 8:19 pm
Posts: 0
Free Member
 

You can have 220v phase to phase, not just 220v to neutral bud, equalling 380 to 415v, like i said not something ive worked on but does crop up!


 
Posted : 20/07/2015 8:49 pm
Posts: 0
Free Member
 

Looks like a nice little unit. There isn't much you can wire wrong really, just connect the single phase input between any two of r s and t and the motor across u v w, the link the motor to be star or delta as required.

Don't get hooked up on the voltages, as its current and frequency that drives motors not volts.

As its giving an output and turning the motor its unlikely to be knackered, so I would put money on it being setup wrong.

The unit has a variable output either from an external input (variable resistor) or using the keypad. In the settings I'd check this first so that a) the output is set it to be by the keypad and b) the output is set it to 100% from the keypad Also check the max output frequency is set to 50hz .

Inverters usually ask for a motor size too to limit the current to a safe value to protect the motor. This might be set too low so check that too.

If the manual is chinglish this might take some time I'm afraid.


 
Posted : 20/07/2015 8:50 pm
Posts: 0
Free Member
 

You can have 220v phase to phase, not just 220v to neutral bud, equalling 380 to 415v, like i said not something ive worked on but does crop up

220 to neutral is 380 line to line just like the spec says.


 
Posted : 20/07/2015 8:57 pm
Posts: 4954
Free Member
 

Vfd usually have a voltage vs frequency curve. You will only get the 220 v phase to phase at 50hz (or 60 hz in N.America) do you have it at full speed?


 
Posted : 20/07/2015 9:33 pm
Posts: 0
Free Member
Topic starter
 

thanks dvatmark,
yep all that's checked and good. not getting hung up on volts, just that the voltage is the only setting that's wrong that's all. and aye, i don't have the supply phase connected accross 2 of RST so that should sort it.
and i know the motor's not knackered. it has to me my wiring or a setting, and seeing as i've sorted all the settings, it's user error, as usual.
right, might go off and change that wiring...


 
Posted : 20/07/2015 9:35 pm
Posts: 4954
Free Member
 

P.s. 220 v three phase exists I north America. At work we have installed a mchaine with 480 and 220 three phase systems


 
Posted : 20/07/2015 9:41 pm
Posts: 0
Free Member
Topic starter
 

that's right, and this is a 380v in y wiring or22o in delta wiring 3phase motor, made for france. they did this so partly so they could sell to america withotu any parts changes


 
Posted : 20/07/2015 9:56 pm
Posts: 0
Free Member
 

My email is in my profile if you need any more help


 
Posted : 20/07/2015 10:02 pm
Posts: 1594
Full Member
 

Looking at the ebay page it's definitely a 220V line-line output voltage and not a 415V, so do make sure that is the kind of motor that you have, otherwise you are going to be in trouble getting it to run at the full rated speed.

Now, talking of the motor, do you have the name plate ratings? And is there anywhere in the inverter settings pages where you can enter these values? Most importantly, the rated voltage and rated speed, and also likely to be the pole number of the motor if you want any idea of how fast you are actually trying to spin the motor!

My guess is that same as a couple of folks above, that the voltage/frequency settings are wrong, and so it's trying to run the motor with too little voltage for a given speed.


 
Posted : 20/07/2015 10:07 pm
Posts: 0
Free Member
Topic starter
 

thanks nick and again dvatcmark.

as i said, the motor is dual voltage, ie it's designed to run ate 380v y-shape wiring, or 220v delta wiring. that's why the converter i bought is 220v 3ph out, to go with the delta option, right?

i have of course used the motor plate to get the relevant ratings and entered them in the inverter settings: max voltage, frequency, speed rpm etc. pole number i couldn't find, though am under the impression it's usually 4, and the inverter factory setting is 4


 
Posted : 21/07/2015 8:45 am
Posts: 2042
Full Member
 

Sounds like you have wired it in star rather than delta.


 
Posted : 21/07/2015 8:53 am
 br
Posts: 18125
Free Member
 

Not sure if it is relevant but when I looked at a 3-phase saw my (electrician) son mentioned something about needing a 3-phase supply to the house - or the 'ability' to get 3-phase from the local electricity sub.

At this point I switched off and looked only at 240v :-), so it could be duff info.


 
Posted : 21/07/2015 8:53 am
Posts: 0
Free Member
Topic starter
 

nope it's definately wired delta twonks. and as far as i understand, in this case delta is for 220v, star, or'Y', is for 380v

just tried bridging the supply phase to the inverter over 2 of the RST terminals as described on ebay listing. made no difference whatsoever.

now i'm really stumped...


 
Posted : 21/07/2015 9:27 am
Posts: 0
Free Member
Topic starter
 

my next line of enquiry is setting 'intermediate frequency/voltage'
these values used to define start-up curve. from readin manual again it sounds like i may need to increase one or the other to get more torque as it's starting up. off to have a go...


 
Posted : 21/07/2015 10:54 am
Posts: 0
Free Member
Topic starter
 

right, so i can now get motor started while connected to the saw and runs up to speed, (though i must admit it seems very fast. rpm is set in inverter according to motor plate though)

i changed the intermediate voltage, ie the curve of the start-up (graph V against F) because in the manual it said wrong setting may result in under-torque of motor.

however it still seems lacking power/torque. and goes very fast as i said. i'd be worried about belts, and whole machine vibrates unsettlingly.

any more thoughts?


 
Posted : 21/07/2015 11:29 am
Posts: 1594
Full Member
 

Jamie..

Can you post the name plate numbers? From those it should be possible to work out what pole number the machine is.

From what you are saying, it does sound like it could be a 2-pole machine, and not a 4 pole.


 
Posted : 21/07/2015 12:59 pm
 mc
Posts: 1198
Free Member
 

Before you start playing with the more advanced settings, go back over the basics.

Single phase should be across any two of the 3 input terminals. What ones doesn't matter, as they all go through rectifiers to provide a DC supply that is then used to generate the 3 phase. The inverter is only interested in seeing 280+VDC in it's capacitor bank.

What does the motor name plate state?
When wired in Delta, you should be using the higher of the two current ratings on the plate.

With the motor running, what frequency is shown on the drive? Provided it's saying 50Hz, the motor should be running at the correct speed (that's provided the motor plate is rated for 50Hz mains supply).
Also check to see how much current is being output (Hz, V and Current are all selectable for the display), and look to see what it maxs out at when you apply a bit load.


 
Posted : 21/07/2015 1:05 pm
Posts: 0
Free Member
 

What's the motor driving ?

Sounds like you have the drive in the wrong mode, needs to be constant torque, it may be in V/F at the moment which will limit torque at low frequency (assuming you have a ramp accelerate program set in it)

Edit: Ignore all that, just read its a saw you are driving

Check and double check parameters !!


 
Posted : 21/07/2015 1:44 pm
Posts: 0
Free Member
Topic starter
 

right, here we go

[url= https://farm1.staticflickr.com/353/19877864192_a7b2ee1a63_n.jp g" target="_blank">https://farm1.staticflickr.com/353/19877864192_a7b2ee1a63_n.jp g"/> [/img][/url]

mc, yes single phase is over 2 of RST. dc voltage reading 300 odd.
plate suggests 220v = delta and will draw 5.9A current.
according to inverter display it was drawing about this til it got up to speed, then went down to 2.9 or thereabouts

with motor running 50 Hz shown on drive

funkynick. any clues there if it's 2-pole or 4 pole?


 
Posted : 21/07/2015 1:59 pm
Posts: 0
Free Member
Topic starter
 

thanks tragically1969. it's actually running a combinaton machine ie saw, spindle moulder, planer/thicknesser. quite a small one though.

anyone know what the cos and symbol spec is above the weight on plate?


 
Posted : 21/07/2015 2:07 pm
Posts: 0
Free Member
 

Power factor.

Can you post a picture of the terminal box wiring ?


 
Posted : 21/07/2015 2:10 pm
Posts: 0
Free Member
Topic starter
 

yes

[url= https://farm1.staticflickr.com/418/19698259240_abeb9364ce_n.jp g" target="_blank">https://farm1.staticflickr.com/418/19698259240_abeb9364ce_n.jp g"/> [/img][/url]
the bit of red on the black wire is just an old bit of sheathing or something.

and here's one of the box drive connections for good measure

[url= https://farm1.staticflickr.com/313/19263622684_e964e6e02e_n.jp g" target="_blank">https://farm1.staticflickr.com/313/19263622684_e964e6e02e_n.jp g"/> [/img][/url]

all looks right, right?


 
Posted : 21/07/2015 2:27 pm
Posts: 0
Free Member
 

looking at the drawing on the Ebay page it may be a switched output, have you checked it is set up to output to voltage you require?

I'm looking at the KA,KB & FC, FA & FB switch set up.


 
Posted : 21/07/2015 2:59 pm
Posts: 0
Free Member
 

looking at the drawing on the Ebay page it may be a switched output, have you checked it is set up to output to voltage you require?

I'm looking at the KA,KB & FC, FA & FB switch set up.

They are outputs for signalling.

Motor is wired delta for sure, just check that the pairs are to the correct terminals, the black wires coming from the windings should be marked.


 
Posted : 21/07/2015 3:27 pm
Posts: 0
Free Member
Topic starter
 

right. think wiring is all correct, thanks tragic
now a new phenomenon
turning on machine with it's own switch trips out the inverter. starting it with it's switch already on, using the run and stop buttons on the inverter, starts ok.
error message when it trips says short circuit. can't see how.

changing intermediate voltage is the only setting which makes any difference at the moment. too much or too little and the motor won't spin up. and it's not affecting running torque, only start-up.

another thing, i can change how many pole motor it is in settings. research seems to suggest it's a 2 pole due to 50 hz and 2840rpm. but it seems to behave exactly the same on either setting. is there a way to tell for sure without pulling the motor apart and looking at configurations of windings?

where do i get those emoticons? damn, there's no :bangs-head-against-wall: one. aaaarrrggghhh. Noying!

the issue's got to be with the inverter right? i bought the machine off my pal/neighbour who has 3 phase and it was working fine. and the wiring is apparently all good.


 
Posted : 21/07/2015 4:48 pm
Posts: 0
Free Member
Topic starter
 

oh yeh, and it's not drawing the current it should when it's running.
2.7a when up to speed and 2 pole setting


 
Posted : 21/07/2015 5:03 pm
 mc
Posts: 1198
Free Member
 

The motor should be wired directly to the inverter, and the switching done via the inverter. Switching the load on an active inverter is pretty much guaranteed to blow the inverter up.

The motor won't draw the rated current unless running at the rated load, and it's perfectly normal for current to increase during acceleration.
What happens to the current reading when you apply some load to the cutter?

2850rpm makes it a 2 pole motor. For a basic inverter setup, the number of poles shouldn't make any difference.


 
Posted : 21/07/2015 6:20 pm
Posts: 0
Free Member
 

As above, there should be nothing in the circuit between the motor and the inverter, they don't like being open circuit, just wire a start/stop button to the run input on the inverter if you want to stop it.

Have you checked to see that all the windings are correct, i.e same resistance and meggered them to earth to check if the insulation is still good ?


 
Posted : 21/07/2015 6:57 pm
Posts: 0
Free Member
Topic starter
 

ok thanks fellas. good info.

i haven't checked the windings and don't know what meggering means.
i will you google it. unles you got a simple explanation how to do it?

finally getting somewhere then. but motor still lacks power.
guess i'll check those things then.


 
Posted : 21/07/2015 8:05 pm
Posts: 0
Free Member
 

Megger, generic term for insulation resistance, put 500/1000V down the windings to check for resistance, or lack of it to earth, but you probably haven't got one of those then by the sounds of it......

If the motor runs its unlikely to be that to be fair, could be that the motor is in fact shot, or you haven't setup the inverter correctly, pretty hard to tell from behind a keyboard to be fair.

NOTE: Disconnect motor from inverter before doing this !!!


 
Posted : 21/07/2015 9:06 pm
Posts: 2661
Free Member
 

your motor plate states 220/380 this means phase to neutral = 220v
phase to phase = 380v
if the output from your inverter is 220 phase to phase you do not have sufficient volts

220 x 1.732=380 (root 3 x 220)


 
Posted : 21/07/2015 10:01 pm
Posts: 1594
Full Member
 

As above, definitely a 2-pole machine.

You said earlier that when you were running the motor without load, it was going faster than you thought it should be, is this still the case when you change the pole number setting to 2?

How are you setting the speed you want? Is it by setting an RPM figure, or Hz?

To me it sounds like one of the inverter parameters isn't set correctly, and that you are trying to run with too low a voltage for a given speed.

Just checking here, if you run the motor unloaded, what does the inverter say it's output voltage is at full speed? And then at half speed? (It's probably best to run this without any intermediate boost etc)

With the two voltages, the first, full speed one, should be double the voltage of the second.

Cheekyboy - the 220/380 means that it can be set up as either a 220V delta wired motor, or a 380V star wired motor. In both of these circumstances you end up with 220V being placed across each coil, because as you rightly pointed out for a star connected system running at 380V gives 220V phase to neutral, which is what the star point is.


 
Posted : 21/07/2015 10:41 pm
 mc
Posts: 1198
Free Member
 

Just checked the manual, and the pole/rpm settings are for user info only, and don't actually affect the running of the inverter.

I'd suggest doing a factory reset on the inverter in case you/somebody else had changed some setting that shouldn't of been, then change only the settings that need changed, which should only be the motor current (PD142). All the other default settings should work fine to test things, and then the only ones I'd be changing would be to configure the start/stop inputs as needed.

As for checking speed, just go by the Hz reading on the display. You can configure the poles/plate RPM so you can see the RPM on the display, but as long as the Hz is at 50, then the motor should be running at the correct speed (squirrel cage motors speed is directly related to the input frequency, so unless the frequency is wrong, the motor speed won't change).

Also, what happens to the current when you apply load to the machine?
How much does it increase, or does the inverter go into current limiting mode?


 
Posted : 21/07/2015 11:41 pm
Posts: 0
Free Member
 

your motor plate states 220/380 this means phase to neutral = 220v
phase to phase = 380v
if the output from your inverter is 220 phase to phase you do not have sufficient volts

220 x 1.732=380 (root 3 x 220)

Utter tosh, its a 3 phase motor hence the voltage is quoted in 3 phase, the Neutral doesn't even figure in it.


 
Posted : 22/07/2015 9:20 am
Posts: 0
Free Member
Topic starter
 

mc
where do you see that pole and rpm settings are for info only. i can certainly change them and when running, the display shows the max rpm i entered.
for that matter, where did you find the manual to look at?

i tried a factory reset and it didn't seems to do it.

not woried about speed any more. it's clearly going at the right speed.

funkynick: "To me it sounds like one of the inverter parameters isn't set correctly, and that you are trying to run with too low a voltage for a given speed."

it seems like that to me too, but still can't figure it out.
i'll go check current under load etc


 
Posted : 22/07/2015 12:12 pm
Posts: 0
Free Member
 

Just on the off chance this, its not a braked motor is it ?

Does the motor just look like a motor or is there anything else bolted to it ?

Look for a torque boost parameter, I am not convinced it should be in V/F mode either more like constant torque but without seeing the exact application its a difficult one.


 
Posted : 22/07/2015 12:29 pm