  • Pellet fired boiler – new system ideas
  • infidel
    Free Member

    So I thought I’d start this thread as there is a lot of forum interest in biomass.

    I’m off the gas grid and heat the house with coal so am changing to biomass. Green deal assessment done – all cavity walls are insulated and I now have 30cm loft insulation. We already have solar thermal on the roof.

    We have had three quotes for systems. These will be housed in a shed in the garden with super-insulated pipe to the house. All three have specified the same size boiler – 15KW. All three boilers are Austrian – Okofen, Biotech and Hapero. I have found a fair bit of information about the first two but very little about the third. I think the Biotech quote is out the window as the company has only been installing for a year or so and were really more interested in trying to sell me an air source heat pump so that leave Biotech – the guy has installed 50 systems in the last 7 years in the area and seems highly competent. He is convinced we need an 800L buffer tank with the system and says that although they can be installed without, the addition of one makes it more efficient. The Hapero guy has installed lots of pellet boilers but this would be his first Hapero. He says no buffer tank is needed. Both systems would be weather compensated.

    I’ve had a long email chat with Stoner and remain a little unsure of which quote to go for. A bit more interrogation of the two quotes to follow.

    Does anyone have any insight into the brands or the use of a buffer? There seems to be a lot of contradictory evidence online about the latter.

    I’ll keep the thread updated as we progress with pics etc!

    Smudger666
    Full Member

    Can’t help with the boilers but the guy is right about a buffer vessel helping make things work well.

    We don’t allow our boilers to be installed without one – doing so invalidates the warranty.

    The boilers will have a minimum modulation point and you will have issues when your heat load is hovering at around that point unless you have a buffer vessel.

    Bear
    Free Member

    Most biomass boilers want you to use a buffer but there are some that don’t. You do need to find someone that understands how to design the rest of the system to work without one though.
    800 litre sounds big for that size system, therefore more expensive.
    I’m no expert but have installed a few both with and without buffers the ones without have worked fine.

    infidel
    Free Member

    The boiler +/- buffer would be in the shed then in the house would be an unvented 300 litre hot water tank which would also have the coils from the thermal solar as well as the coil from boiler/buffer. I wonder if the Hapero guy is considering the hot water tank to be enough for a buffer in itself?

    Bear
    Free Member

    No it wouldn’t be, total different thing.

    You really need to zone your heating and remove controls from rads etc to ensure minimum load is covered by each zone. It is a bit more complicated but if you are starting your system from scratch then it is do-able. However you sound like you are adding boiler to existing system so a buffer is probably required, but I would question the size.

    metalheart
    Free Member

    Buffer vessel is critical for the operation of biomass. The load fluctuates and once you have a biomass lit what are you going to do with heat from the unburnt/remainder of the pellets in the boiler itself when the load drops off?

    A buffer allows the load to be kept fairly constant and keep your boiler firing efficiently, turn down is not great for biomass (even worse for wood chip but that’s irrelevant here).

    The problems that I’m aware of with installed pellet boilers I’d be leaning towards someone who has as much experience as possible.

    Just my 2p worth.

    Bear
    Free Member

    Buffers are critical for MOST systems, but you can make them work perfectly acceptably without.
    I know of a system that is working faultlessly without a buffer. Minimum run times are being comfortably exceeded by the 35kW boiler, no overheating issues either.

    Stoner
    Free Member

    The load fluctuates and once you have a biomass lit what are you going to do with heat from the unburnt/remainder of the pellets in the boiler itself when the load drops off?

    There are lots of pellet boilers out there now that dont use buffers – they have sufficient modulation of control and water in the boiler to deal with energy over run. Log burners on the other hand are uncontrolled burns and so do need a buffer.

    My neighbour’s Okofen has no buffer and copes fine, yes it cycles, but newer boilers are much better at handling cycling. The pellet component of mine does not like cycling much, but then I have a big buffer so that it might only fire twice or three times a day in the middle of winter. My neighbour’s might fire 10-20 times a day.

    infidel
    Free Member

    We are modifying the existing system. We plan to keep the rads. These will be on one circuit and all have TRVs. The towel rads will be a separate circuit.

    Bear – other than pushing up the price,would an 800 litre tank actually cause problems? I will ask the system heating engineer how he got to 800.

    Bear
    Free Member

    No problem using a big buffer, there are more readily available than smaller ones. If you are keeping rads with TRV then buffer us needed.

    Stoner – I wouldn’t want one that cycles that much.

    Stoner
    Free Member

    neither would I. Mine runs best at full chat for 700Litres of snuggly hot water.

    infidel
    Free Member

    I think that’s me decided then. I’ll keep this thread updated with build pics etc

    PS – re sheds and power poles on my thread from the other day, the electricity board came round and have said that they want a 1 meter distance between a shed and the 240 V pole. It’d have been a very different matter if it was an 11000 V pole.

    metalheart
    Free Member

    Ok, how does turn down effect efficiency?

    Does pellet suffer from volatiles issues like wood chip?

    Not really much experience in the domestic market (although I now have an ESCo agreement to buy heat produced by what might even be an Okofen. Which has a buffer by the way).

    OP: apologies for the digression/hijack.

    infidel
    Free Member

    Quick update – I called the Hapero guy who I was not planning to go with and he made a strong case to support his system design and has agreed in writing to install a buffer tank for free should the system require one. He says it will be obvious looking at the boiler computer whether it has been short cycling and would then install a buffer. He seems a genuinely decent guy who is keen for the job and I have to confess I am sorely tempted. At his price I could put a 2KW solar PV system on the shed roof to supplement our solar thermal system too and to keep the boiler fired if we had a power cut (during the day only I accept!).

    Difficult decision time especially as despite lots of research I am not at the end of the day a heating engineer.

    infidel
    Free Member

    Thread resurrection – finally getting things on the move with the pellet boiler.

    It’s been a hell of a thing so far and a lot to learn. So far I have had to learn about boiler types and brands. Quite a lot of the on line info is continental so heavy use of google translate and a big thankyou to Stoner too.

    I’ve also learned about vented and unvented systems and subsequently about water pressure and flow rates and THEN about accumulator tanks and pipe diameters….

    so.

    I had a hole in the ground:

    and this week put a slab there:

    Blockwork this weekend – pics to follow. Thank god my neighbour is a retired builder ‘cos I am learning hard and fast!

    Smudger666
    Full Member

    Just read your update two posts ago…

    If your PV system is grid connected, then you aren’t going to get anything out of it if there’s a power cut. They need the grid to work.

    You’d be cheaper and more reliable if you get a lot of power cuts to fit a generator and manual switch over to power the boiler/pump/zone valves.

    Separate building for your ‘energy centre’ is a great move though!

    And just to agree with bear about the buffer – it CAN work without a buffer if you get someone who isn’t just connecting pipes to an existing system with no engineering the system to suit biomass – would be interested in seeing any schematics the installer has provided.

    mrmonkfinger
    Free Member

    m off the gas grid and heat the house with coal so am changing to biomass.

    out of interest, what coal system did you have before switching?

    Stoner
    Free Member

    I am learning hard and fast!

    ’tis the best way.
    Good luck, keep the photos coming.

    infidel
    Free Member

    Hi Guys.

    So we currently have a 21KW multifuel boiler stove which predominantly runs on homefire ovals and some wood. It came with the house and has a couple of issues:
    1. there is no back protection to stop cold water coming into the boiler.
    2. the central heating circuit is injector t’d off the hot water circuit and short cycles a fair bit until the whole system is up to a good heat.
    3. Out house is cut into a bank with the driveway at the top and the main living area / boiler at the bottom if the bank. So far this year I’ve carried over 2 tonnes of coal down the bank and the resultant ash back up the bank. I’m not sure I can face doing that for the next 20+ years!

    I’ve discovered the bit about the PV’s going off in a power cut now. They really don’t happen much around here so I am going to see how we do without a backup generator but have space to install one if needed. We are installing a controller that will automatically feed any electricity we generate and which we are not using into the immersion element in the hot water tank. That will augment the solar thermal we already have on our roof in the summer so I can just turn the pellet boiler off.

    The boiler is a Hapero 15KW unit. The manufacturers and installers are convinced we will not need a buffer and have written a statement that should the system short cycle they will supply and install a buffer for free. The plan is to rip out the existing hot water thank and its vented associated gubbins and replace with a larger unvented hot water tank, new plumbing to link into the rads and uniting the current heat sink radiators into the main rad circuit. This is also requiring a cold water accumulator as although we have good static pressure and pressure/flow with 1 tap open, it falls with 3 taps to 6l/sec flow and pressure of 0.5 bar.

    Think that’s it for the mo. Blockwork pics to come when I can and shed framing starting Tuesday (I hope)

    mrmonkfinger
    Free Member

    We had pretty much the same setup, except our boiler stove was in no way capable of reaching its rated output, and we rarely got out of the short-cycling phase. It was ok, sort of, when we had dry wood, I guess, but a massive faff – far too much manual tending/loading/emptying required.

    Didn’t have the space or cash for a pellet unit, so we went with a TRG coal unit, which does at least have the magic of automatic controls.

    Smudger666
    Full Member

    nice.

    re-connecting the PV to the immersion – good idea – recommend them when the meter doesn’t go backwards.

    I had a couple of comments about the Unvented DHW cylinder typed out but realised that it would sound like I’m looking for your installer to cock up, which I’m not – they do sound like they’ve done this before.

    a cracking set up – If i wasn’t living in a bungalow with mains gas, i’d be adding a pellet boiler to the current solar PV/Thermal already installed.

    I’d be really interested in the final project costings and your EPC numbers when you are done.

    infidel
    Free Member

    Morning! The brickwork is done and its time to get framing:

    hope to have this lot out of the carport soon..

    Smudger – I’d be keen to hear any comments/advice re unvented systems. The installers have done loads of these but more knowledge is never a bad thing and I’d rather ask them questions before irreversible/difficult to undo stuff happens!!!!

    The project is expensive but thats in part because I want to do it right and so it fits in with the rest of the house (ie the outbuilding is oak clad) and the RHI is offsetting much of the cost.

    sharkbait
    Free Member

    recommend them when the meter doesn’t go backwards.

    Anybody with PV and a meter that runs backwards is running a risk.

    The leccy supplier will eventually find out and they can then send you a back dated bill for the power they reckon you’ve ‘stolen’ – their calculation will be heavily in their favour.

    Smudger666
    Full Member

    sharkbait – yup you are spot on – which is why i kept a copy of my email asking them specifically about the meter going backwards, sent to them on the day i had the PV installed asking them if I needed to take any further action 😉

    Infidel – the points i was going to mention are about the lack of buffer and what they had calculated to use as the heat sink. i then noted you had plans to link the heat sink radiators to the system so I assume the design for the heat dump from the boiler would use those.

    I’ve seen one where the heating engineer planned to use the cylinder as his heat sink as he did on ‘all his solid fuel systems’, and the plumber installed an unvented cylinder. They decided that it would be ok to miss out the MZV on the DHW flow pipe to ensure the heatsink was always available. Once they’d been made aware of the practical safety aspects and the legal ramifications of doing that, they went back and installed a heat sink radiator.

    mrmonkfinger
    Free Member

    heating engineer planned to use the cylinder as his heat sink as he did on ‘all his solid fuel systems’

    Misuse of word engineer there, I would say.

    Smudger666
    Full Member

    fair point – think ‘bloke who had installed solid fuel fireplaces since the 1890’s and thought he knew better than hetas/building control’ and you’ll be on the right lines!

    infidel
    Free Member

    Got the bulk of the framing done today. I’ve never done it before so it took some time. My neighbour popped round this evening and helped me do the support struts to square it up and stabilise prior to the rafters etc.

    I’ve looked at so many ‘I built this’ threads here (Stoner and McMoonter come to mind) and never thought I’d be able to do similar!

    infidel
    Free Member

    Raftering going up. 22.5 degrees dead south facing for the PV roof. I’d have liked to go a bit steeper but I didn’t want the north roof any steeper and wanted to limit the building height.

    cbike
    Free Member

    The freakonomics guys pointed out PV panels would earn more pointed west for supplying at peak times rather than during the day.

    Is stuff like that taken into consideration or does total duration earn more?

    Smudger666
    Full Member

    Cbike – with the uk tariffs – as near South as possible for max production is best.

    Infidel – 22.5 vs 35 degrees – you’ll hardly notice the difference. When we’ve modelled production in the past, anything above 15 degrees didn’t really affect production enough to worry about.

    Looking good!

    Stoner
    Free Member

    *clicks the Share Like button*

    sharkbait
    Free Member

    Cbike – with the uk tariffs – as near South as possible for max production is best.

    It could be argued though that to get the best out of PV you want to use as much of the generated power as possible. Although down overall very slightly on S facing panels, an E & W orientation can give more power when you need it. For example, E facing panels supply power early in the morning when people are getting up, while W facing panels can supply more power in the evenings – again when it’s needed most.
    S facing panels generate peak power at lunchtime when domestic power requirement is generally lower than morning/evenings.

    infidel
    Free Member

    Its been a busy week with work and I’ve been away so it’s been a bit slow. Raftering is done, roof joists in and framing is complete with what I now know to be called noggins!!!

    properbikeco
    Free Member

    great work, we all love build threads like this so keep the pictures coming

    infidel
    Free Member

    Big update time.

    So I’ve called in the cavalry as there is lots here that I cannot do.

    The shed roof has been started and the walls membraned. The roof is sheet boarded on the big south roof and lathed only on the north:

    The walls are now being cladded:


    Cladding to be finished and roof to do… on the outside..

    Inside:

    boiler is the big grey box, the blue thing is the cold water accumulator and there’s a new hot water cylinder too (twin coil)):

    boiler being plumbed in and the cold water cylinder is plumbed in now:

    The hot circuit connects to the house across a big gap – the hot in on the right as you look at it, the cold on the left:

    and finally, today, the hot water cylinder is in, although only basically plumbed tonight:

    Stoner
    Free Member

    good work!
    Im actually v jealous. It’s a lot of fun. Takes me back:

    [img]https://lh4.googleusercontent.com/-_vvna01dwEo/TgjoO8-ofuI/AAAAAAAAAB4/vHykkJCH0D8/s400/p1000551.jpg[/img]

    Edukator
    Free Member

    Double or triple lag all those pipes, please. 🙂

    project
    Free Member

    Worked at a house haveing a pellet system installed, a few questions, does the boiler need to be insulated or heated when switched off when not in use in winter,to prevent freezing, do all external pipes need to be protected by wooden insulated boxing,to stop theft or damage, some nice copper pipes exposed, is blown deliveries cheaper than sack deliveries of pellets, cheapest time to buy pellets.

    infidel
    Free Member

    Edukator – yessir! Stoner – you have been a bit of an inspiration for this and I used a few of your threads to work out how to get started with the shed too!!

    Its exciting but a bit daunting as there is so much to learn to make sure its done right. We’ve gone from a vented to an unvented hot water system today and the house is a bit cold tonight as the multifuel burner is currently disconnected. The living room open fire is roaring and our daughters have plug in oil radiators tonight!

    paul4stones
    Full Member

    Very impressive. Love it.

    Very late but just to say we have a Windhager which was a straight swap for an oil combi. No buffer but an unvented hot water system already in place. Been in three years now and it’s great.

    Looking forward to the rest of this now!