With some decorating coming up I decided to move a radiator to a better location in my room. The previous rad had never worked properly, I’d always assumed it was blocked (was a fairly old rad) so it was a good reason to improve the location and get rid of what I thought was a fault rad.
-Installed the new rad / lockshield & TRV and I’ve struggled to get the rad working properly.
After closing off all other rads in the system to remove what I thought was an airlock I’m 99% certain the rad is plumbed in series off the rad in the adjacent room (would have ‘made sense’ as they did share the same wall)
With every rad in the house closed bar the two plumbed in series I was finally getting some (although not a lot) heat to the new rad.
When I open up the other rad’s in the house I’m losing all flow to the new radiator (2nd in the series and the last rad on the heating circuit)
I’m resigned to re-plumbing correctly to the main feed/return – before do I have any other options / or anything I’ve missed in my fault diagnosis!?
I’m getting frustrated!
Thanks.