As a rough rule of thumb – you need 50m2 per kW of heat load.
If you are gutting it, and reinsulating to at least current minimum building regs, then you can (again, rough rule of thumb) assume 50W/m2 – so a 150m2 build, will have a peak heat load of 7.5kw, requiring 375m2 of ground loops.
Remember the above is a very rough guide – ground thermal conductivity will vary by the ground type – sand/gravel needs more area, wet soggy loam may need less.
Best to get an expert to quote/design.
Btw, the slope is irrelevant regarding the pipes/pump – its a closed loop so what you pump up the hill, falls down the other side.
Also, make sure the heat emitters – rads or underfloor are sized to suit the flow temp of the heat pump. Rads typically trebled in size, underfloor centres at 150mm.