Viewing 4 posts - 1 through 4 (of 4 total)
  • Electrickery – cable for 3kW max
  • sharkbait
    I need to replace a short piece of cable [literally less than 2 x 20cm sections] that carry a maximum of 3kW (Immersion).
    I have some spare 1mm twin and earth hanging around – the internets says that’s fine but I thought I’d ask on here* too.
    * Fully expect to be told that I should have the whole house rewired, shouldn’t drive a big diesel, that my lawn needs cutting and it’s all the government’s fault.
    SSS
    Without going to look at my copy of the BS7671…….
    Yes, you are correct – ‘clipped direct’ the current carrying capacity exceeds your requirement of 12.5A (3kW @240v)
    Source https://intrelec.co.uk/2020/10/21/cable-sizing-charts/
    Its very short so volt drop shouldnt be an issue.
    BUT! The cable will have been calculated on fault current/ protective device rating etc
    So would i use it?
    No.
    Id be looking at 2.5mm probably for an immersion (i think the regs say 1.5mm minimum)
    temudgin
    The cable connecting to the immersion should be heat resisting- butyl flex would be ideal.
    sharkbait
    It’s actually going near the CU in another room so heat is not an issue.
    Ahh, fair enough. I do actually have a roll of 2.5mm but it’s just a PITA to deal with as it’s ‘so’ stiff! I was hoping to get away with something more flexible – not to worry, 2.5mm it is!