  • Any electricians on board? I need to hard wire a cooker 6mm or 10mm cable?
  • eggbanjo
    Free Member

    New cooker arriving on Thursday an AEG 49002VMN and needs hard wiring.
    It has double oven and 4 ceramic hobs
    Total load is 11.4 kw
    50 Hz
    fuse size is 30 amp
    will 6mm be okay or should I go for 10mm
    I’m not sure what cable is running from the consumer unit to the outlet in the kitchen. Should I check it and just go with that?

    paladin
    Full Member

    You’ll need to know what size has been run from the consumer unit.

    When I put in new hob, I had to put a bigger cable in.

    TheOtherJamie
    Free Member

    11.4kW is 49.5 Amps

    You’ll be needing a 10mm from the consumer unit plus new fuse/mcb and 50A cooker switch

    snaps
    Free Member

    30 amps is less than 8kw – you’ll also need to calculate volt drop, if its as long cable run, you might even need 16mm

    trail_rat
    Free Member

    Sounds like you want to get a spark in . Too many questions in this post – scares me to give vague answers to vague questions incase you start a fire :/

    TheOtherJamie
    Free Member

    you’ll also need to calculate volt drop

    10mm will do 50m at 5% volt drop.

    RaveyDavey
    Free Member

    Am with trail rat on this. If you have to ask then you shouldn’t be attempting it. Are there rules against wiring yhem yourself if you aren’t qualified?

    dannybgoode
    Full Member

    @RD – I think there are now. Didn’t used to be but its changed.

    TBH with the kind of current that is involved consulting a sparky is probably very sensible….

    simonbowns
    Free Member

    call an electrician. It’s life and death.

    bruneep
    Full Member

    trail_rat – Member
    Sounds like you want to get a spark in . Too many questions in this post – scares me to give vague answers to vague questions incase you start a fire :/

    FFS! give him answers anything, it keeps me in gainful employment.

    trail_rat
    Free Member

    Haha – thanks to a bodger you were about 2 showers from coming to my gaff before i rewired.

    Previous Idiot wired my 10.5kw shower in on 8mm cable( despite changing it to 12 from the fuse board to the pullcord….) and it had started to burn the live wire insulation back down the cable.

    Its now on a real rcd system instead of wire fuses and 12mm cable from the box to the shower unit.

    gears_suck
    Free Member

    Yeah, I don’t know how we’ve all lived this long before all the regs and HSE got involved. Every 9.5 kW shower ever fitted on 6mm cable should have burned and killed everyone within a ten block radius.

    dibboid
    Free Member

    FFS! give him answers anything, it keeps me in gainful employment.

    I presume you’re a fireman. 😀

    trail_rat
    Free Member

    [Img]https://lh3.googleusercontent.com/-5jewRF1QjGw/UPVYl-K6ptI/AAAAAAAAHjc/Lk2BexySmFM/s288/%255BUNSET%255D.jpg[/img]

    What my shower looked like after tripping the fuse board. Worth the risk ?

    gears_suck
    Free Member

    TR that could well be due to a loose terminal which will cause overheating regardless of correct or incorrectly sized cabling.

    trail_rat
    Free Member

    Could also have been a small smurf starting a fire under it.

    Ill stick with speccing the correct sized cable via the maths instead of guessing at what should be fitted from “experiance” or “its working isnt it shut up”

    waveydave
    Free Member

    +1 for ‘theotherjamie’.
    chances are that your cable back to the consumer unit will be 6mm judging by your 30amp fuse. get a recommended sparky to sort you out.

    @ trail rat – that cable in the pic looks like 2.5mm to me

    trail_rat
    Free Member

    You might be right – it was rediculously underspeced i remember that much .

    Much like my entire garage being wired into a lighting circuit from the back bedroom – and being signed off by building control. Loved that part.

    Buying someone elses house is awesome.

    gears_suck
    Free Member

    Errrr. Yea TR keep yer pants on there little fella. I wasn’t saying it was right. Merely pointing out that even the correct sized cable overheat if the terminals aren’t pinched up tight enough. It’s as much the installation as the materials. Both have to be right..

    eggbanjo
    Free Member

    Thanks guys, think ill get a sparky in.

    Dales_rider
    Free Member

    6 mm

    flap_jack
    Free Member

    We bought one of these 2 weeks ago. The manual says use 6mm. You won’t get 10mm into the connector in the back of the cooker, it’s optimised for 6mm.

    Bacuase of the decorative state of the house, I can still touch the cables. Not even warm with everything flat-out.

    But, still get a sparky in.

    astormatt
    Free Member

    It will more than likely be fine on 6mm, apply diversity then see what you get.

    marcus
    Free Member

    I wired in an AEG in last year. I cannot remember the model number of the unit but the fitting insructions specified a very unusual specification of 10mm ‘flex’ which I couldnt even find to buy despite hours of googling. Consequently its on 10mm twin and earth.

    trail_rat
    Free Member

    Astormatt – genuine question here as it didnt apply to my cooker at the time due to kitchen layout.

    Diversity as i understand it is for things dual rated where you cant draw the max rated load as it would involve 2 or more systems working against each other. Hence why you cant apply it to a shower as its a single system drawing the load.

    Surely i could cook on all 4 hobs and have the big oven and little oven on cooking a xmas dinner and draw 11.4kw

    Unless of course they have added the grill system into that where it would be impossible to have it on when the ovens on.

    alanl
    Free Member

    trailrat is about right.
    Diversity will apply to a cooker, so you will use the first 10 amps, plus 30% of the remainder to get your cable / overcurrent device size.

    11.4kW is 49 amps.
    So 10 A plus 30% of 39A = 10A + 13A = 23A
    Your cable will need to be able to carry 23A continuous.
    Current carrying capacity of 6mm T+E cable is around 47A if buried in plaster, with no insulation around it. If bunched with other cables, its capacity drops, so assume it has a little insulation, or is bunched, so it will now have a current carrying capacity of 32A.
    Which is perfect for your existing installation, as your new cooker will be a direct connection to the existing installation.

    There’s a caveat that the Manufacturers installation instructions must be observed. They may require the use of a RCD to protect the cooker, so, in your case, having a fuse as your overcurrent device, I doubt if you have RCD protection on that circuit.

    So simplistically, your existing installation will be fine, if the manufacturers instructions do not want RCD protection.

    alanl
    Free Member

    Trailrat to answer your question, it is very unlikely that all elements in an oven will be on at one time, and when they are, it is not for long, as they are all thermostatically controlled, so once up to temperature, they do not draw full power for long.
    If you have an electric oven, this is easily seen/heard when the thermostat clicks to turn on/off the element.

    There are occasions when all will be drawing full power, but the duration will be so short that it will not put enough load through the overcurrent device, for long enough, to trip it.

    A 32A breaker will not trip at 33A. At 50A it will think about tripping after 15 minutes. You need to put 160A through it for near instant tripping, they are there for fault protection instantly, and overcurrent protection over time – the characteristics are that they trip before the cable melts.

    trail_rat
    Free Member

    cheers for that alan.

    crofts2007
    Free Member

    trail_rat – Member
    Haha – thanks to a bodger you were about 2 showers from coming to my gaff before i rewired.

    Previous Idiot wired my 10.5kw shower in on 8mm cable( despite changing it to 12 from the fuse board to the pullcord….) and it had started to burn the live wire insulation back down the cable.

    Its now on a real rcd system instead of wire fuses and 12mm cable from the box to the shower unit.

    POSTED 16 HOURS AGO #

    Where do you get 8mm and 12mm twin and earth from?

    takisawa2
    Full Member

    10mm when I wired in our 10.8kw shower. Had to uprate the pull cord also. That cable takes some man handling too. 😯

    Wasnt keen on wiring it in with old fashioned fuse wire type fuse, so bought a new consumer unit for it to go in to. (Was cheaper than a stand alone 50A unit).

    In fact, must get round to wiring the rest of the house into the new consumer unit also. 😳

    dibboid
    Free Member

    Thermostatic shower and a gas cooker Ftw. Best thing I ever did was ditch the electric shower. 🙂

    highclimber
    Free Member

    If you can get away with using 6mm then it will be a hell of a lot easier to handle and install than 10mm cable not to mention cheaper too though the price should be the least of your concerns where electricity goes!

    Try this calculator to work out what you *might* need

    Dales_rider
    Free Member

    Sat wondering how much the sparky has charged or did he stand there making that sucking noise through his teeth whilst shaking his head then start his first sentence with “Well”