As the link explains, a burst water main.
Low Pressure gas mains typically run at somewhere between 25 and 50mbar, a little higher if all plastic systems. High pressure water leaks can blow holes in metallic and plastic gas pipes, allowing water to flood the relatively low pressure gas network.
This has to be removed. Once clear & repaired the gas system has to be purged from air to gas. Before this is done all properties served by the affected system should be capped off at the meter, or services physically disconnected where there is no access, to avoid the risk of gas passing into the property. Re-commissioning has to be done progressively to prevent an explosive gas/air mix. This takes time if it is to be done in a safe, controlled manner.