Viewing 40 posts - 1 through 40 (of 47 total)
  • STW plumbing/heating engineer collective – underfloor heating advice required
  • smogmonster
    Full Member

    Folks, the benefit of your collective wisdom please. Our underfloor heating doesnt seem to playing ball at the moment. It heats the downstairs (obviously), but seems to be heating only our guest room and ensuite, at the far end of the house. Our lounge, kitchen and utility are not heating at all, the floor remains cold. Thermostats are set to 20C..it doesnt make any difference where we set them, nothing changes. The boiler is a Combi, with the settings for the heating at 6 (out of 9 settings) and again, it doesnt appear to matter where its set at, the above areas remain cold. Hot water is being produced without issue.
    Ive had advice from a mate of a mate that underfloor needs leaving on permanently to work, which sounds like bollocks to me, is this correct? The thought of it blasting away from now until kingdom come fills my bank account with horror. As we are in and out at various times, we have it set to turn on and off at the usual times (0600 – 0900, 1100 – 1400, 1700 – 2230).

    Anyone help us out, either professionals, or anyone with a similar problem resolved?

    sugdenr
    Free Member

    UFH has a reaction time between something like 12 and 24 hours depending if you have slab underneath or on top of the insulation. But regardless it a thermal mass heating system not a radiator(technically they are convectors not radiators), you have to keep it warmed up to work. The idea is to use low grade heat (30 to 55 deg depending) rather than the 60 deg that rads need to ‘blast out’ enough heat. Condesning boilers stop condensing at about 55 deg.

    However sounds to me like you are not getting any flow to parts of your system, check the distribution maniflold isnt closed off etc, otherwise get someone in to check it.

    chickenman
    Full Member

    As above, UFH pipes are embedded in 2″ of concrete, water is at blood temperature but is tempered down to this beyond the boiler. Since pipes are plastic and 15mm, they are unlikely to block. Different zones may have seperate pumps and timer channels; is something out of synch there?
    Room stats only need to be at 17c as the heat is round your feet (where you need it!).
    I have mine on from 6am to miday then 5pm till 1am. The boiler barely ticks over most of the time so it shouldn’t hit your gas bill.

    Stoner
    Free Member

    wot sug sed ^

    check manifold valves are balanced correctly. And run it at 40deg ish for 6hrs.

    wrecker
    Free Member

    Check manifold(s) as it sounds too localised to be a warm up problem (could be wrong)
    Actuator could have failed, ports could be blocked.

    smogmonster
    Full Member

    Cheers all, ive just had a fiddle, and the thermostats dont ‘click’ (turn on?) until they are set to 23C…is this right? If not, anyway of lowering this?

    Stoner
    Free Member

    do you have thermostatically controlled manifold valves or manual ones like lockshield valves?

    what are these “thermostats” of which you speak? How many? Where? Attached to what? How?

    wrecker
    Free Member

    Bi metal switch probably.
    If its not clicking until 23 deg, it thinks it’s 23 deg in the room.
    Without looking at it, I don’t know if you can calibrate it.

    smogmonster
    Full Member

    Stoner – not a scooby tbh. There is a bunch of valves and pipes in a cupboard tucked away in a recess in the lounge. There are 3 wall mounted thermostats, one in the guest room, one in the lounge and one in the kitchen, each with temperature dials…which seem to ‘click’ when i tuern them to 23C.

    Stoner
    Free Member

    can you take a pic of the manifold?

    I assume then that you have room thermostats that open or close motorised valves on your manifold.
    as wrecker says, if the bimetal strip is responding to “23degs” then it’s either 23 degrees in your house or you thermostats are a little out, in which case set them to, say, 18degrees + 23degrees – current temp.

    sugdenr
    Free Member

    that mass of pipes, feel them, are there some hot and some not?

    wrecker
    Free Member

    Hmmm. I see you have stats in the kitchen and lounge, which means that they are probably not controlled by the same valve. Does the UFH heat up when the stat is made?

    Stoner
    Free Member

    BTW – I bet you can pull the dial off the thermostat and push it back on at a different rotation to zero it.

    wrecker
    Free Member

    Good thinking stoner, although many have stops I think.

    Stoner
    Free Member

    I think the stop would be on the stem/controller not the dial face wouldnt it?

    d’You reckon independant motorised valves on the manifold controlled by room stats?

    smogmonster
    Full Member

    Folks, pics of the manifold, pipes and thermostat.

    Stoner
    Free Member

    right.

    looks like 6 zones, (6 grey cables). If there are only 3 thermostats then I assume that there are 2 zones per room.

    uponor motorised valves

    Why is there a thermostatic valve on the supply side? Is it a crude “mixer” as opposed to a flow and return blending valve? That white twiddly thing on the left needs to be open, i.e. the air temp needs to be below the setting to allow hot water to flow to the manifold. seems a weird place to have one.

    To check everything is working, turn the three thermostats up high so they switch.

    Turn the white twiddly thing up high so its not restricting flow and then check that whatever is controlling the flow pump (white wire to the grey pump) is turned on.

    You should see the flow gauges (black towers on the top of the manifold) all showing a flow rate to each zone.

    * whats written on the piece of wood?*

    smogmonster
    Full Member

    The wood just identifies where each pipe supplies..2 for utility/kitchen, 2 for lounge, 2 for guest room/ensuite.

    Thanks for the advice, i’ll try your suggestions and see how it goes.

    TheFunkyMonkey
    Free Member

    wtf is that TRV doing? blending valve is top right stoner, above the pump.

    check the flow rates as said and just feel the pipes. if they;re all hot, then you have one of two things.

    1) blockage, unlikely

    2) the thermal mass the pipes are in is not having enough time to warm up

    Stoner
    Free Member

    blending valve is top right stoner, above the pump.

    you sure?

    looks a very odd one.
    ANyway, I still think that TRV is in an odd place.

    TheFunkyMonkey
    Free Member

    i reckon so, think the knob is missing. not sure what the small box is

    Stoner
    Free Member

    just seems odd to have the “box” so far away (3″ above) the valve

    TheFunkyMonkey
    Free Member

    no idea hat that box is, looks out of place. only 15mm flow and return from/to the boiler also

    Bear
    Free Member

    Don’t turn the thermostatic valve up on the left it is how the water temp is managed by the underfloor. Turn it up too high and you will cook your floors possible damaging coverings and it is also unhealthy.
    Is should be set according to your floor type.

    I assume the underfloor has been working ok? If so it is something that has changed, usually an electrical component gone wrong, open up all the room thermostats and see if the heads open on the manifold. You should be able to tell because the window on the gauge on the return manifold will show a flow rate change.
    Turn the room thermostats as high as they will go to make sure they are calling for heat. Remove cover and check with a multimeter to see if they are sending a signal.

    Check to see if you have a supply to the manifold pump.
    Check manifold pump is rotating.
    Investigate the manifold junction box if nothing obvious has been found yet.
    The system pump (in the boiler probably) could push the water round one u/floor loop but is probably not man enough for the whole system hence checking u/f pump.

    You could have air trapped in a loop or two.

    You could always ask a plumber who knows a bit about u/floor to have a look, most of the manufacturers have a recommended list for a certain area. Happy to help more if you like.

    mail me at timATj-twren.eclipse.co.uk

    Stoner
    Free Member

    the more I look at it the more I dont get why that pump is where it is…

    am I going mad?…

    Bear
    Free Member

    I believe that box on the left is also some kind of thermostat. Worked on one of their systems for the NHBC a while ago (also fault finding on it). Will look out details as think I took some notes.

    TheFunkyMonkey
    Free Member

    probably doesn’t matter, but shouldn’t the TRV be on the flow side if it is performing that function? I don’t see how it could possiblt contol the flow temp in any case, isn’t that what blending valves are for? esp on ufh systems

    Stoner
    Free Member

    Don’t turn the thermostatic valve up on the left

    so it’s not an air thermo valve, but a water thermostatic valve then?

    well thats just silly. Im not thinking.

    Bear
    Free Member

    how do you know it isn’t on the flow.
    think the box on the right hand end is an overheat stat.

    TheFunkyMonkey
    Free Member

    good point (smartarse) 🙂

    Stoner
    Free Member

    then whats blending the supply heat down to useable heat.
    That trv isnt doing it.

    TheFunkyMonkey
    Free Member

    yeah, get a man in.

    has it ever worked properly?

    Bear
    Free Member

    Yup it has a capillary with a probe on the end that should be connected to one of the manifolds. It doesn’t blend it limits the available water temp. A lot of manufacturers use this method, nice and simple, cheap and easy to repair.

    Bear
    Free Member

    A thought the overheat could have tripped if the control valve has been turned up / capillary dislodged.

    I believe the overheat stops the underfloor pump (system pump would maybe make one loop work as i mentioned earlier)

    Stoner
    Free Member

    ah, so the capillary link is replacing the air temp function?

    Much prefer a nice mixer valve myself 😉

    Anyway, I think we’re all agreed on the method to identify which bit isnt working.

    all thermostats on, pump on, check for flow rate in each zone. then work from there.

    Bear
    Free Member

    Stoner – I have used David Robbens systems for ages now, they used to use mixers, got rid of them as uneccesary and another valve to go wrong.
    I’ve tried other companies but they have been a great company to work with, I even get to try out some new things for them on some of my projects sometimes!

    Bear
    Free Member

    Oh and just fitted a 35kW Windhager biomass on a job, know you like your pellets!
    (was bloody heavy!)

    Stoner
    Free Member

    35kW Windhager biomass on a job,
    (was bloody heavy!)

    no shit ! 😉

    another valve to go wrong.

    same could be said of the TRV 😉

    Ill get a pic of my manifold etc up tomorrow. Mines much dumber as I dont need zonal control and it has a thermal store supply.

    Dobbo
    Full Member

    Look familiar?

    More info.

    TRV is on primary boiler flow circuit not UFH secondary.

    TheFopster
    Free Member

    At risk of oversimplifying, I don’t suppose it could be anything as simple as an air-lock could it? Just a thought, but UFH systems can get them. If so a quick flush through could sort it?

Viewing 40 posts - 1 through 40 (of 47 total)

The topic ‘STW plumbing/heating engineer collective – underfloor heating advice required’ is closed to new replies.