Firstly, check the power shower’s pump rating. I would guess it’s around 500W. This equates to about 2amps load so 1.5mm FTE is fine run from an FCU with a 3 or 5 amp fuse.
The FCU should be outside zone 2 – ie further than 0.6m from the edge of the shower/bath.
The RCD should be rated at 30mA.
The pull cord is not really a requirement as you’ve got a point of isolation with the FCU. I’m guessing the pump only runs when the water flows so it’s not like an electric shower which would need a suitable isolator.
If you’re replacing like for like there is no requirement for notification to building control unless it’s in a special location (ie a place containing a bath or shower). However, if the pump’s under a floor somewhere it’s could be argued that it’s not a special location.
Obviously it’s difficult to give guidance without actually seeing the job so “caveat emptor” or the electrical consultancy equivalent applies.
Any questions, just ask.
Rich.