1. Critical Safety Areas.
1. Critical Safety Areas. The areas of internal and external walls which are considered ‘critical locations’ in terms of safety are:
1.1 Between the finished floor level and 1500mm above that level in doors, and in side panels which are within 300mm of either edge of the door.
1.2 Between the finished floor level 800mm above that level in the case of walls, partitions and windows. 2. Requirements of BS 6262 Part.
2.1 Safe Breakage: For doors and door side panels, the glazing used should not break, or should break safely in accordance with Class C of the standard impact test BS 6206(1981) if 900mm wide or less, or Class B if wider than 900mm.
For other low level glazing the pane should comply with at least BS 6206 Class C.Use laminated or toughened glass, or plastics glazing sheet, or wired glass, that meet BS6206, or glass with plastic film applied so the pane of glass with film meets BS6206