RCD stands for Residual Current Device.
It sits across the Live and Neutral wires in your consumer unit (used to be called the “fuse box” and it monitors where the current is flowing too. Under normal conditions, every amp that flows out along the Live wire is expected to come back down the Neutral wire, ie sum to zero. When an earth leakage fault occurs, ie something becoming Live that shouldn’t be, and hence current flows out to Earth, instead of Neutral, then the RCD trips (should be within around 30ms) to try to prevent the risk of electric shock. This device is in-addition to the normal fuses, or these days circuit breakers, that open the circuit is excessive current flows (but flows the right way around the circuit, ie Live to Neutral.
So, if your RCD is tripping immediately then:
1) the RCD is faulty – not that un-common, they have sensitive relays and electrical / mechanical bits inside.
2) Current is leaking out to earth (as little as 10mA possibly to trip a typical 30mA RCD)
I had a friend who’s RCD would trip after heavy rain, and eventually, after much searching, they found a hole in a cable in the shed onto which rain water would drip, but only after very heavy rain, and the current was using that water as an escape route to Earth, hence the RCD tripping
As others have said, it’s a matter of isolating each circuit in turn to find the one that trips the RCD, bearing in mind the RCD itself could be faulty!