An oversized store will have a number of negatives
1) at 1.16 wh/Kgk of water, 10 degree mains temp and an AVERAGE water temp in the tank (allowing for stratification) of say 60 degrees (don’t forget you want to maintain a cold temp at the bottom of the tank to make the most of any solar collection), then your tank would hold around 70kWh of energy. that’s quite a lot to be trying to take out of a back boiler even before replacing consumption. Back boiler likely to be rated no more than 2-5kW.
2) 1200 litres is a lot to try and get up to a usable temp in the top layers from solar.
3) that’s a lot of inhibitor to replace anytime you need to drain down
4) draining down will take a fortnight 🙂
Edit Bear is your man in here for sensible sizing advice.