Static possibly, and what has not been mentioned is high earth leakage current.
Does the circuit have a RCD?
Have you got other IT/TV equipment plugged into the same circuit?
If no RCD, and other kit plugged in, then you may well be getting a belt from the equipment.
RCD’s typically trip at 20-25mA, they are designed to trip before 30mA, most trip sooner.
An old computer ‘leaks’ around 8mA of current to the earth pin, and the casing of the computer. TVs/DVDs/Wiis can also leak current. Generally, any metal cased hi-tech kit will be leaking current directly to earth, other stuff does too.
If you havent got a good earth connection, either at the plug connection, or at the fuse box/consumer unit, then the current may find ti easier to go through you than works its way around the house back to the main earthing terminal at the meter/fuse box etc.
If this is happening, then you should be looking at putting another (extra) earth conductor in for that circuit, or, checking you have good connections throughout the circuit.For a typical office, this is usually designed in. It is only the last 10 years that such equipment has become prevalent in houses, and people come across this problem occasionally.
If it is static, then ignore all of the above.