  • Electrician help needed …. dimmer switch question
  • danjthomas
    Free Member

    I have a single landing light run from a 2 way dimmer switch at the bottom of the stairs and a normal single switch upstairs. The light is just a typical rose with a standard 40W light bulb.

    The problem is that the light is flashing constantly and doesnt react to dimming, howver does improve if i turn it up full and press the dimmer switch sideways hard!!

    Do i need a new switch or do i have a comparability issue here?

    leffeboy
    Full Member

    What would the ‘comparability’ (compatibility?) issue be? You say it is a standard lightbulb but do you mean a low energy or a regular filament lamp? Also has it just stopped working whe it worked before or has something changed?

    Mikey65
    Free Member

    Get the connections checked in the switch…replace the dimmer with a normal switch (only a couple of quid)see if problem goes away…replace dimmer if it does, if you want to.

    leffeboy
    Full Member

    Oh well. As Mikey65 says, replace the dimmer with a normal switch. Not sure why you would want a dimmer on a landing – especially for a 40W bulb. I’ve seen funny flashy things before with dimmers and low energy bulbs but not regular bulbs. However I did notice that the last dimmer I put in had a minimum load of 60W which surprised me so it may be that your bulb is too small