  • Cold radiator. Why?
  • Harry_the_Spider
    Full Member

    Heating is on. Valve is open. There is water in it.

    The feed pipe is hot, the drain isn’t.

    Any ideas?

    maccruiskeen
    Full Member

    does the pressure doofer on the boiler need re-pressurifying. Thats what mine needed

    maccruiskeen
    Full Member

    does the pressure doofer on the boiler need re-pressurifying. Thats what mine needed

    (it needed doing twice)

    Stoner
    Free Member

    TRV stuck closed.

    Unscrew the thermostatic body and give the pin a tap and wiggle.

    muckytee
    Free Member

    Bleed it?

    paulosoxo
    Free Member

    Valve type? TRV? Possibly the pin stick down.

    Normal wheel head valve? Bleed air, shut off the rest of the rads and force heat through

    donald
    Free Member

    Stoner +1

    Cougar
    Full Member

    Might need balancing? (I am not a plumber)

    midlifecrashes
    Full Member

    If it’s just started doing this, TRV

    If it’s always like this, or on a house you don’t know, maybe flow balancing problems

    totalshell
    Full Member

    wtaer is not circulating something is stopping it.. stoner is probably right.. if the poin does go up and down turn off all the other rads and open the clod one wide open to force the issue if no joy .. phone call time..

    allthepies
    Free Member

    Have you bled any air out of it ?

    Harry_the_Spider
    Full Member

    No air in it.

    How do I free up a stuck TRV?

    Stoner
    Free Member

    you still here?

    WackoAK
    Free Member

    Could be a blockage, might be some rust in the system. Had this in a rental flat years ago and the chap who came round to check it hit the exit pipe with a spanner and it worked..

    wors
    Full Member

    Turn all thermostats off in the house except the cold one, it will have an air lock in the pipe somewhere. That’ll blast it through.

    paulosoxo
    Free Member

    Harry_the_Spider – Member
    No air in it.

    How do I free up a stuck TRV?

    POSTED 23 MINUTES AGO # REPORT-POST

    Head should screw off

    Pin should push down and spring back, if it’s stuck down, then that’s the issue.

    Pulling the pin up is no good, as often the the valve seating is seperate.

    A mixture of drops of wd40, tapping valve side, and pushing down on pin will free it.

    If you pull the pin out too far, it’ll come out of the valve. Followed by the water.

    Harry_the_Spider
    Full Member

    Pin is springy. Gave the other end a whack with a 12mm hex wrench. Going to do the same to my missus if she keeps telling me it isn’t working.

    unovolo
    Free Member

    Trv valve stuck
    Rads need balancing
    Air lock (either in the rad or the system)

    We had this in the rad in the dining room,turned out to be the rads all needed balancing,upstairs rads getting hot to quickly and the dining room rad is the last in the circuit .
    Took a bit of trial and error to get it all working.
    Numerous guides to balancing rads on the net.