  • Boiler condemned – advice needed
  • MrPottatoHead
    Full Member

    Hi, quick bit of advice needed on boilers. We moved into our house a year ago. When buying the house we asked for boiler to be serviced by the owners and this was done. It had been installed in 2010.

    Today had a guy out to do an annual service and he immediately spotted a problem with the original installation that he felt was bad enough to condemn the boiler. Basically the casing had been drilled to route the electricity cables, instead of using the correct inlets with rubber grommets. This means the case is no longer airtight which presents a risk. He spoke to the manufacturer on the phone & with my consent he has disconnected and made safe the appliance and advised a new one was needed.

    I have since checked the gas safe register and the original installation was never registered, which makes me think the installers may have known there was an issue. I’m not sure there’s much that could be done after this length of time though.

    I guess my question is; does the reason for condemning the boiler seem sound or should I try and get a second opinion & who from? Who could provide a definitive answer?

    We have a 2 year old so I don’t have the luxury of messing about on this. SSE have already been out and quoted for a replacement. £2300 fitted (bye, bye new bike). I’m sure there’s a big premium on using them but at least they can fit quickly and are ‘including’ some extras worth about £600. Does this seem too extortionate though?

    glasgowdan
    Free Member

    Was it SSE that ‘condemned’ it?

    Get a local gas safe guy out. Worst case scenario you need a new boiler and it’ll cost a grand less than the SSE quote. And guess what – sole traders can fit a boiler at short notice too! Under a day work.

    garage-dweller
    Full Member

    Sounds pricey to me to my non specialist mind, at least get another quote.

    We had a new boiler in with our extension a couple of years back 4bed, 3reception,2 bathroom house and boiler figure was comfortably under that iirc.

    spooky_b329
    Full Member

    Can you get a new case as a spare part, and get the supply rerouted correctly?

    Nipper99
    Free Member

    Our British Gas fitter told us where and what boiler to buy and he then fitted it. Valiant Ecotech 28 was 750 plus vat and 1200 fitting by BG.

    allthepies
    Free Member

    This is why I avoid getting the boiler serviced in winter.

    Bear
    Free Member

    as suggested, new case, route cables correctly.

    What boiler out of interest I’ll look up the case price if you like.

    andyl
    Free Member

    Couple of things:

    Seems a bit fishy to me as I’ve never seen a boiler with air tight casing. Get a decent local guy to come and take a look.

    Call the boiler manufacturer and send them photos, they might be able to suggest a fix or maybe an IP rated cable gland would suffice?

    Your solicitor should have obtained a copy of the gas safe installation certificate. Sounds like they have missed something. Also the person who serviced the boiler should have noticed, check that they are gas safe registered as if not there is an offence there too.

    MrPottatoHead
    Full Member

    This is why I avoid getting the boiler serviced in winter.

    Indeed – I’m blaming the wife for this one! It was a local gas safe guy who came out this morning and he would be getting the work if he hadn’t quoted a 4 week wait on his availability.

    Nippers pricing sounds about same figure I’ve been quoted. I was surprised fitting would be so expensive. I’ll definitely try and get another local quote; its just SSE were quick to get out.

    Would labour charges on new case also be high – assume its pretty much a new install when you replace that?

    Flaperon
    Full Member

    The casing on a gas boiler isn’t supposed to be airtight. It’s a metal box to hide the stuff inside. Can you post up a photo?

    allthepies
    Free Member

    The casing on my old (1990 install) Potterton boiler is required to be airtight due to the ventilation design. Modern boilers probably don’t have this flaw!

    http://www.miketheboilerman.com/Netaheat.htm

    See “Safety Warning:” section 🙂

    MrPottatoHead
    Full Member

    Will upload pics once i get wee man in bed. Its a Vaillant Ecotec 612.

    dvatcmark
    Free Member

    [Quote]The casing on a gas boiler isn’t supposed to be airtight. It’s a metal box to hide the stuff inside. Can you post up a photo[/quote]
    +1

    Surly the case being air tight would be more dangerous, as any leaking gas would get trapped inside

    andyl
    Free Member

    There is no way that casing is airtight (assuming it’s the plus model here): http://www.vaillant.co.uk/downloads/new-2015-boiler-manauls/system/ecotec-plus-612-615-618-624-630-spares-manual-664858.pdf

    Get some pics up. Call gas safe and tell them everything as if it’s been done by a dodgy installer then they will want to know and may well help you with getting it looked at again and if the SSE guy is trying it on they may also be interested in that.

    chickenman
    Full Member

    Does sound like a bollocks overreaction to me. Surely the burner is in a sealed box and if the outer casing needs to be sealed (some sort of flue balancing thing?) then that can be sorted with sealing around the cable hole?

    MrPottatoHead
    Full Member

    Pics

    Main unit with cover off;

    Electricity feed is being the electronics panel;

    Hole drilled for cable;

    northernmatt
    Full Member

    Seems a bit drastic to get a new boiler because the casing has a hole drilled in it.

    That bottom panel should be available separately, I could check if I was at work., but as you say it may be a ball ache to change over. Had a quick look at install instructions and it looks like the cable should come in on the left and through to the control box at the front. I have no idea if this would pass a gas safe inspection but is it not possible for reroute the cable correctly and use some silicone to bung the hole up?

    wrightyson
    Free Member

    1200 quid for fitting is an absolute piss take! Just had my plumber supply and fit a new boiler for my dad for 1200 quid.

    dvatcmark
    Free Member

    I’m no boiler expert but I really struggle to see why that would condem the boiler. I’d be speaking to vailents tech support before committing to a new boiler.

    Is the other side of that hole just on the outside of the boiler case or is there some sort of box section there ?

    stumpyjon
    Full Member

    British gas condemned and disconnected our one year old boiler for the same reason. Ironically fitted by my wifes heating engineers. The casing is supposed to be somewhat air tight, however this is really only a secondary precaution in case the boiler malfunctions and starts spewing out carbon monoxide. It should go out the flue not into the room. Just seal around the cables, silicon or similar or better still get some grommets. Then find a more sensible person to service it.

    bigad40
    Free Member

    Are you kidding!!!!!???
    There’s nothing wrong with that!!
    Did the guy who condemned that give you a warning notice?
    I will drop in and sort it out if you are local.

    wrecker
    Free Member

    WTF? Fit a grommet/gland or silicone it up!
    It is very bad form running cable through a hole drilled in metal without one, but if all the gas safe bloke is concerned about is tightness, bloody seal it up or even reroute the cable and seal the hole!
    Jeez.

    bennn
    Free Member

    New boiler not required, fit one of these – (http://www.screwfix.com/p/tower-male-comp-gland-white-20mm-pack-of-2/45943) and have it serviced by someone else.

    MrPottatoHead
    Full Member

    Thanks for the replies. Based on what you’re saying I’d agree it does seem overkill, which I guess is the dilemma. If I’ve got one Gas Safe registered engineer saying it needs to be condemned, who is then in a position of authority to say they were wrong? Do I just keep getting out engineers until I find one who agrees with my view?

    I’ve emailed the pics to Vaillant but will try and speak to them in the morning too. I’ll also give Gas Safe a call and see what advice they can provide.

    allthepies
    Free Member

    Once it’s been “condemned” then good luck finding someone who will sign off a repair to an original bodge. Massive ass-covering will come into play.

    fluxhutchinson
    Free Member

    Tbh he’s right, whether you think its stupid or not. Send an email to vaillant they may or may not approve a grommet. Ideal have done in the past, wheres remeha wouldn’t for a problem that was created by a design flaw.

    Bear
    Free Member

    I’m not so sure that that the case doesn’t form part of the balancing chamber for combustion on that boiler, think it is the case with the spring clips and also the case has a foam seal on it from memory.

    If that is the case then yes that hole would condemn the boiler as it forms part of the combustion chamber.

    project
    Free Member

    gas safe are your freind, theyll ivestigate dodgy practices and overcharging for the sake of it, also sse probably get commision for every boiler they sell install. Did he actually speak to Valliant, or his boss pretending to be Valliant.

    hora
    Free Member

    I had an issue with gas safe/corgi over a cert etc. Appalling to deal with, seemed to side step all help. My local council however brought the fitter to task very quickly.

    OP if I had your situation I’d be calling in a second opinion. Even if an extra £70 confirmed the other blokecwas right it’s piece of mind over a big rectifying spend.

    singletrackmind
    Full Member

    ok , assuming that the air around the boiler forms an airtight pre- combustion chamber , then look on ebay for a Gas safe engineer to do a like for like swap ( I paid £550 this way , incl a machine power flush ). then source a combi for the bst price , either WB , Vailiant or Ideal appear to be the current favs’s.

    Or Buy a new outer case and get a Gas safe or NIC certified sparky to supply the juice without drilling a massive hole in it .

    Simples.

    mick_r
    Full Member

    It is just a bit of metal – undoing the bodge and making it airtight should be perfectly possible. Replacing a functioning quality boiler of that age is madness.

    And you are being ripped off on the fitting. We had a new Worcester Bosch combi installed last week (in place of old one but needed some pipe mods, new flue hole etc). Easy single day job and £150 for labour. All in with new (expensive) boiler, filter, chemicals, longer flue, pipes VAT etc less than £1500.

    I understand your urgency as we just managed a week without any heating or hot water (it gets easier after a few days). Kettle took some hammer (be careful with the 2 yr old and all that boiling water) and a couple of £20 2kW convector heaters from B&Q were surprisingly effective!

    fluxhutchinson
    Free Member

    Who says its a rip off price just because you got some moron to fit yours for £150?

    pictonroad
    Full Member

    Am I missing something? It’s a small hole. Disconnect the wire, pull it out, route the wire properly and repair the hole.

    I’m really not trying to be obtuse but I cannot see any reason that can’t be really simply fixed.

    mick_r
    Full Member

    Who says its a rip off price just because you got some moron to fit yours for £150?

    No I got a trusted Gas safe registered and well established local guy to fit mine for his regular northern england day rate of £150. Only downside was waiting a week (as he was busy on other jobs, like all good tradesmen). And as I understand what was involved in the job I did all possible prep beforehand to make his work quick and easy.

    £2300 for a straight combi swap is a rip off.

    fluxhutchinson
    Free Member

    Well I’m regular northerner too 😉 Minimum £500 atm to swap a combi plus materials and sundries.

    Good for him if he can make that work but I know lads that at the higher end of the scale are getting £1200 a combi swap + Boiler and materials (Granted their few and far between).

    Cougar
    Full Member

    If it helps,

    AFAIK, “condemned” means “can’t switch it back on until it’s fixed” rather than “you need a new one.” My system’s been condemned several times.

    wrecker
    Free Member

    My system’s been condemned several times.

    😀
    Try a different engineer!

    MrPottatoHead
    Full Member

    That’s useful to know. He’s marked it as Immediately Dangerous so from the Gas Safe site it does seem a repair could be acceptable. I’ll see if they can confirm what an acceptable repair would be but hopefully just re-routing and fill the bodge.

    ‘Immediately Dangerous’ (ID)
    An “immediately dangerous” installation is one which, if operated or left connected to a gas supply, is considered to be an immediate danger to life or property.

    The installation will be disconnected, with your permission, and must not be used until the necessary work has been carried out to repair the defect(s). If you continue to use an immediately dangerous installation you could be putting you or your family’s lives in danger.

    fluxhutchinson
    Free Member

    Gas safe can’t do anything. Vaillant and Vaillant alone will be the only ones going to be able to make a decision. They may even offer to do a repair/ replace the bottom panel Although Im not sure its removable on this model.

    I take it the engineer has capped the gas supply at present?

    griptool
    Free Member

    That Boiler has a negative pressure case so don’t worry too much.
    The gas engineer was correct in applying a safety notice as the integrity of the combustion seal has been compromised, however, as I said above the boiler is negative pressure so air is going in rather than fumes coming out.

    If your gas fitter were to take a pragmatic approach he would seal the inappropriate cable entry with a non setting compound (FJC,or equivalent) and all would be fine.

    Having said that, there are 3 cable entry points on the bottom of that boiler, so why the installer decided to drill (or let his feckless sparky drill it!!) is beyond me.

    If you do have a new boiler fitted, I’ll give you 20 quid for the old one,,, 😉