Ahh Tootall, just the man.
Pressure at meter is about 19.6 at full power and Struggles to make 17.4mbar at the gas valve. Pipe work was all 22mm and now is a mixture of 28 and 22mm.
Currently have:
meter, 22-28mm, 90deg, 90 deg, <0.8m, 90deg, 1m, 90 deg, 1m, 90deg, 1.6m, 45deg, 0.3m, 90 deg.
Then 28-22mm and into the concrete floor where the route and condition is unknown. Hall way is 6m long, and then we have about 3m to the middle of the living room and then 3m to where I have picked it up under the living room floor.
Then I have in 22mm: 90 deg, 0.5m, 90 deg, 0.2m, 90 deg, 1.5m, 90 deg, 0.6m up into boiler.
Looking at the manual it states the 30CDI will take down to 18mbar but the 30Si will take down to 16.5mbar.
There is no mention of the total drop for the 30CDI (installer tells me it should be 1mbar) but the manual for the 20Si states 1mbar from meter to inlet and then 1.5mbar to valve allowing a total of 2.5mbar.
It was suggested to me that in retrospect the 30Si would have been a better choice due to the pressure drop. Or is this wrong and with either I will have to replace all the pipes?
So close to removing the whole thing and fitting some electric heaters and renting it out cheap to compensate for the crappy running costs of electric.